Topic Title: AOV Manual Override and Panel
Topic Summary: Locations
Created On: 13 April 2018 11:55 AM
ArduinoXR
Can somebody point me in the direction of some relevant info on requirements for AOV manual override switches and panels please? Sanity check more than anything.
 15 April 2018 06:02 PM
burn
BS EN 12101-2:2017 Smoke and heat control systems. Natural smoke and heat exhaust ventilators
Should tell you everything you need to know. If you have access to a copy of course.
It can vary depending on the position of the vents, the type of building and the how the smoke ventilation is designed to work.
As a general rule, the fireman's overide should be just outside the protected (vented) area, on the fire brigade's intended route in.
The control panel can go anywhere.
burn