IET logo
 
IET
Decrease font size
Increase font size
Topic Title: Sub main
Topic Summary:
Created On: 23 March 2015 09:12 PM
Status: Read Only
Linear : Threading : Single : Branch
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 23 March 2015 09:12 PM
User is offline View Users Profile Print this message



21stcentury

Posts: 19
Joined: 18 December 2011

Hello folks, just a quick query. Building with 12 flats, intake position in basement plant room along with ryefield, seperate metering and switch fuse for each flat. SWA cable from switch fuse to each flat.
Are the swa sub main cables under the scope of ena er g87 and/or bs7671? Initally i thought that unmetered cables and not sub mains are under the scope of ena er g87....is that correct? Thanks in advance
 23 March 2015 09:52 PM
User is offline View Users Profile Print this message



nad

Posts: 410
Joined: 14 January 2005

They're in a building so all defiantly under BS7671. They are also service cables so fall under G87 (DNO) and Energy Supplier / MOp rules. Your the customer side of the Meter so I can't think of anything in G87 that wouldn't be required in BS7671? You will need to terminate the SWA in a 6x6 trunking, with the correct slots cut in to marry up with the meter positions and sleeve the cores as they pass from the trunking to the meter. Contact EDF energy and ask for metering standard details. There are also standard layouts in the WPD SD5C doc.

-------------------------
Nad

*Regularly edited due to spell cheque misdiagnosis
Statistics

New here?


See Also:



FuseTalk Standard Edition v3.2 - © 1999-2018 FuseTalk Inc. All rights reserved.

..