Hello
What it the content that a battery discharger report should have? Thank you very much |
|
|
|
|
|
|
|
|
A Battery dischage test draws a fixed current for a certain period of time. At the end of the test the battery voltage should not have dropped below the precalculated minimum voltage.
You normaly take individual cell voltages and specific gravitys every hour. You can hire machines that you hook up set up and press go and it does every thing for you, except take the SG's. |
|
|
|
|
|
|
|
|
In addition to the above we like to see a visual condition assessment of the battery and its installation.
Prior to starting the test the battery voltage and charging current is also measured. The report would also then need to make recommendations for any repairs that may be required to bring the system back up to specification. Kind regards Donald Lane |
|
|
|
|
|
|
|
|
I also like the battery discharger reports of the Amperis unit since it also includes the graph of the battery voltage and you can see how it slowly diminishes as the test goes on.
|
|
|
|
|