IET
Decrease font size
Increase font size
Topic Title: Radar Tower Adjacent to 11000V Substation
Topic Summary:
Created On: 25 June 2012 08:11 PM
Status: Post and Reply
Linear : Threading : Single : Branch
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 25 June 2012 08:11 PM
User is offline View Users Profile Print this message



MickeyB

Posts: 149
Joined: 18 January 2003

Had a query about the location of a new radar tower adjacent, say 30m away, from an existing concrete/ brick enclosed 11kV substation...

My view was that the tower, suitably connected to general mass of earth via the foundation piles and dedicated copper/ steel earth rods to BS EN 62305 would not cause a problem for the substation, rather the tower would help 'divert' any potential strike away from the substation and mitigate the effects.....

Provided the substation had its own surge suppression devices to cover an incoming strike (from outside the substation) everything should be fine.... any comments to the contrary....
 31 July 2012 02:01 PM
User is offline View Users Profile Print this message


Avatar for timothyboler                                      .
timothyboler

Posts: 205
Joined: 25 July 2008

For a more certain response you'd have to provide some more information; there's no simple answer with this one; although I agree with properly installed surge devices and a low enough ground resistance you would at least protect the equipment if not the structure.

What class of lightning protection system is required?
How high is the substation compared to the tower? Is it within the 'rolling sphere'?
What lightning protection does the substation have? Where would the surge arresters be installed?
Are overhead lines being used?
What is the type of earthing system?
Are the radar tower and substation earthing systems interconnected?
Are the HV and LV earths in the substation interconnected or separated?
What is the combined resistance of the HV, LV and radar tower earthing electrodes/pile foundations (measured as isolated systems)?

Depending on the details it could be a yes or a no.

Regards, Tim

-------------------------