Topic Title: BS5839
Topic Summary: Call point requirements
Created On: 01 May 2013 09:28 PM
Status: Post and Reply
Linear : Threading : Single : Branch
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 01 May 2013 09:28 PM
User is offline View Users Profile Print this message


Avatar for leckie.
leckie

Posts: 1806
Joined: 21 November 2008

Doing a public house, including a fire alarm. Bit concerned about having break glass call points by the exit doors as I can imagine them being hit by people after a couple of halves of Mackeson Cream Stout.

BS5839 refers to the omission of BGCP's to "some Public Houses".

So do I fit them or omit them?
 01 May 2013 10:00 PM
User is offline View Users Profile Print this message


Avatar for Rulland.
Rulland

Posts: 461
Joined: 11 April 2008

Fire officer/consultant recommended call points behind bar and by kitchen door on a small bar/bistro I did recently, For the same reasons as you pointed out.

-------------------------
Those who make no mistakes do very little work!!......
 01 May 2013 10:06 PM
User is offline View Users Profile Print this message


Avatar for leckie.
leckie

Posts: 1806
Joined: 21 November 2008

That's exactly what I was thinking, thanks.
 01 May 2013 10:33 PM
User is offline View Users Profile Print this message



DOUGIE1000

Posts: 4164
Joined: 13 August 2005

What's wrong with the flip up covers?

-------------------------
Dougie
Power Plus Electrical.co.uk

My mission is to live as long as possible......so far so good!
 02 May 2013 07:11 AM
User is offline View Users Profile Print this message


Avatar for leckie.
leckie

Posts: 1806
Joined: 21 November 2008

The only specification I received was for it to be L2, no fire officer or consultant involved. Its a freehouse and the owners have just asked for a fire alarm to be fitted. I could fit flip up covers I suppose. I just thought it would be a potential problem.

BS5839 it a bit ambiguous as it says "some" public houses. Any opinions on what this might mean? It might mean a busy city centre pub perhaps, as opposed to a standard "local". This is a quiet pub so perhaps it would be ok to fit them. I'll have to do some undercover work and visit lots of pubs. For research only you understand.
 02 May 2013 12:28 PM
User is offline View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 19625
Joined: 23 March 2004

They should be at the exits generally - even if not fire exits - if you omit them (which is allowable under BS 5839 - 1) then that is a variation to be recorded - and I would get your client to agree that with the enforcing authority.

If you fit them and use flip up covers, they become two stage devices and again you'll need to record that as a variation.

I've used both options subject to a RA from the client and agreement with the enforcing body.

I wouldn't omit them or add flip up covers without either client or enforcing body confirmation in writing (and ideally both)

Regards

OMS

-------------------------
Failure is always an option
 02 May 2013 09:31 PM
User is offline View Users Profile Print this message


Avatar for leckie.
leckie

Posts: 1806
Joined: 21 November 2008

Well I've installed all the provisional wiring so I think I will fit them and if they require omitting at a later stage I will blank off. I haven't got time to wait for fire officers, etc. Many thanks all.
 03 May 2013 06:31 PM
User is offline View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 19625
Joined: 23 March 2004

Fire rated connectors if you do connect thro' and blank off -

regards

OMS

-------------------------
Failure is always an option
 03 May 2013 10:12 PM
User is offline View Users Profile Print this message


Avatar for leckie.
leckie

Posts: 1806
Joined: 21 November 2008

Of course OMS! Actually had a fire officer out and he said leave them out but put a call point behind the bar and one in a public area but not by the exits. But I will check with whoever dishes out the licence.