hi all , went to a property today to install a garage supply carried out zs at nearest socket 208 ohms !,checked service head , just two very old what look like 16 mm cables poking through a wooden board one to a neutral block, one to a service fuse, 2.5 earth cable coming up through floor to MET ..... now before you all scream tt i have never come across tt in my town (fleetwood,lancs ) ever, the service cable must come through the wall from next door (who wasnt in !) terraced housing in my area all have tncs or tns, the property has no rcd protection so have suggested the contact dno to request engineer ( no rcd unit in van and wholesalers shut )last one like this neighbour had new board fitted by friend and had snipped the looped earth from their MET.

-------------------------
master of puppets is pulling your strings
--------------------------------------------
http://www.elliselectricalservices.com
 16 February 2013 05:54 PM
User is offline View Users Profile Print this message


Avatar for slittle.
slittle

Posts: 3587
Joined: 22 November 2007

I'd go for TNS on a looped service and as you've already said missing from next door


Stu
 16 February 2013 09:09 PM
User is offline View Users Profile Print this message


Avatar for UKPN.
UKPN

Posts: 541
Joined: 17 January 2012

looped lateral main-best if DNO give PME to your installation.
 16 February 2013 09:27 PM
User is offline View Users Profile Print this message



John Peckham

Posts: 7579
Joined: 23 April 2005

Might be an old water pipe earth below the floor connected to the bare copperconductor.

-------------------------
John Peckham

http://www.astutetechnicalservices.co.uk/
 16 February 2013 10:06 PM
User is offline View Users Profile Print this message


Avatar for stateit.
stateit

Posts: 2220
Joined: 15 April 2005

If memory serves me correct several years ago I had faults presenting themselves in house 1 traced back to faults at house 2 with a looped main. Took me a while of head scratching.

-------------------------
S George
http://www.sg-electrical.com