 12 September 2012 08:23 PM
User is offline View Users Profile Print this message



TopTrumper

Posts: 157
Joined: 22 July 2006

Hello Fellas,
A bit of a question for all you P.I.R type of guys out there.

I never bother with writing reports, but just possible that i might do a few in the future.

Now I can tell you how things have to be installed in these regulations and the 16th.

What I would like to know is, if you get called to report on an installation, and its in perfect condition to 16th, but no RCDs, what happens?
 12 September 2012 08:36 PM
User is offline View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 17584
Joined: 23 March 2004

Well, you examine the installation against the 17th edition - lack of RCD's in an otherwise OK install is usually a Code C3 - Improvement Recommended. It's up to you to take a view on sockets, buried cables and bathrooms/shower rooms

This would still allow you to give the installation a "satisfactory" for its continued use.

regards

OMS

-------------------------
Failure is always an option
 12 September 2012 08:43 PM
User is offline View Users Profile Print this message



TopTrumper

Posts: 157
Joined: 22 July 2006

Thanks OMS
Just refamiliarising myself with codes...seriously, its all changed..
but the new ESC leaflets are quite good.....
 13 September 2012 02:24 AM
User is offline View Users Profile Print this message


Avatar for spinlondon.
spinlondon

Posts: 4375
Joined: 10 December 2004

I t would depend on whether there was a requirement for RCD protection at the time of construction.
If not then as OMS says, code C3.
If there was, then code C2.
 13 September 2012 06:21 AM
User is offline View Users Profile Print this message



johnboy6083

Posts: 29
Joined: 25 July 2008

i disagree spin. I feel that the codes refer specifically top whether there there is danger present or not.

So a C2 is for a situation where a fault would cause an increased level if danger, if a particualr saftey measure that is in the regs is not present.

So i would code lack of RCD on sockets that supply mobile equipment for us outside ect as a code 2, whether the house was wired last year or in the 30's.

However i would code sockets upstairs in a bedroom with no RCD for protection from screws ect as a C3
 13 September 2012 07:34 AM
User is offline View Users Profile Print this message


Avatar for zeeper.
zeeper

Posts: 1213
Joined: 11 July 2008

Q]Now I can tell you how things have to be installed in these regulations and the 16th


Forget the 16th. When you are filling out an electrical installation condition report your view point is from the latest edition of the regulations.

C1 Danger present, risk of injury, Immediate action required.

C2 Potentially dangerous - urgent remedial action required.

C3 Improvement recommended

Take your pick.

common sense says C3 , however is it any different than say a MCB oversized for the cable csa which in my book would be C2. If the protective device is incorrect for the level of protection required must be C2. But, if you turn to page 80 of your GN3 amendment 1 table 3.5. absence of RCD specified for addition protection C3.

However i would code sockets upstairs in a bedroom with no RCD for protection from screws ect as a C3


I had to smile the other week when walking back from the takeaway. there was a gentleman hovering out his car. The extension lead hanging out of the secound floor window of a small block of flats .
 13 September 2012 11:51 AM
User is offline View Users Profile Print this message



Jaymack

Posts: 4291
Joined: 07 April 2004

Originally posted by: zeeper
there was a gentleman hovering out his car.

Had to smile also. Height above ground? Means of suspension?

Regards
 13 September 2012 03:30 PM
User is offline View Users Profile Print this message


Avatar for spinlondon.
spinlondon

Posts: 4375
Joined: 10 December 2004

Originally posted by: johnboy6083
i disagree spin. I feel that the codes refer specifically top whether there there is danger present or not.

So a C2 is for a situation where a fault would cause an increased level if danger, if a particualr saftey measure that is in the regs is not present.

So i would code lack of RCD on sockets that supply mobile equipment for us outside ect as a code 2, whether the house was wired last year or in the 30's.

However i would code sockets upstairs in a bedroom with no RCD for protection from screws ect as a C3

You start off disagreeing with me, then end up with the same result?
 13 September 2012 04:11 PM
User is offline View Users Profile Print this message



AJJewsbury

Posts: 9785
Joined: 13 August 2003

You start off disagreeing with me, then end up with the same result?

Not entirely. Under spin's scheme it would be a C3 if it was constructed in 2007, but a C2 if the installation was physically identical but constructed in 2009?

- Andy.
 13 September 2012 09:13 PM
User is offline View Users Profile Print this message


Avatar for spinlondon.
spinlondon

Posts: 4375
Joined: 10 December 2004

Originally posted by: AJJewsbury
You start off disagreeing with me, then end up with the same result?

Not entirely. Under spin's scheme it would be a C3 if it was constructed in 2007, but a C2 if the installation was physically identical but constructed in 2009?

- Andy.


Conversly, you could have an installation which was constructed in 1970 which if tested in 2007 would have warrented a code 2, but if tested in 2009 no code at all.
 13 September 2012 10:16 PM
User is offline View Users Profile Print this message



AJJewsbury

Posts: 9785
Joined: 13 August 2003

Conversly, you could have an installation which was constructed in 1970 which if tested in 2007 would have warrented a code 2, but if tested in 2009 no code at all.

Indeed. I re-wired my previous house in the to early days of the 16th (just before bathroom zones came in), so the bathroom had supplementary bonding between all extraneous-conductive-parts (and had there been any, exposed-conductive-parts), but not to c.p.c.s to circuits which supplied all-insulated accessories (as the lighting happened to be). I also happened to add 30mA RCD protection to all circuits. So it complied with the early 16th, didn't comply with the later 16th (as there was no bonding to c.p.c.s), but come the 17th (where supp bonding can be omitted) complies again.
- Andy.
 13 September 2012 10:43 PM
User is offline View Users Profile Print this message


Avatar for spinlondon.
spinlondon

Posts: 4375
Joined: 10 December 2004

I was atually thinking more along the lines of RCD protection for socket-outlets.
The 16th required any socket-outlet that could reasonably be expected to supply portable equipment outdoors to be RCD protected, whereas the 17th only requires socket-outlets for use by ordinary persons and intended for general use to be RCD protected.
 14 September 2012 10:24 AM
User is offline View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 17584
Joined: 23 March 2004

Originally posted by: spinlondon

I was atually thinking more along the lines of RCD protection for socket-outlets.

The 16th required any socket-outlet that could reasonably be expected to supply portable equipment outdoors to be RCD protected, whereas the 17th only requires socket-outlets for use by ordinary persons and intended for general use to be RCD protected.


Are you missing 411.3.3 (ii) - by definition mobile equipment is likley to be used from a socket outlet up to 32A - if it's for use outdoors then we need the 30mA RCD.

Regards

OMS

-------------------------
Failure is always an option
 14 September 2012 12:16 PM
User is offline View Users Profile Print this message


Avatar for spinlondon.
spinlondon

Posts: 4375
Joined: 10 December 2004

The requirement is to provide RCD protection for: "mobile equipment with a current rating not exceeding 32 A for use outdoors."
The requirement could be met by use of an RCD plug.
However, that is not my point.
The 16th requirement was directed at any socket which could reasonably be expected to be used for such a purpose.
The 17th is directed at only such sockets that are actually used for such a purpose.
Unless you have evidence that indicates a socket is actually being used to supply mobile equipment outdoors, there is no non-compliance.
Take for instance a couple of LU switch rooms that I recently worked on.
There are about nine DBs spread across the two rooms.
Each DB has had a single socket attached for the specific pupose of testing the Zs at each board.
As these are the only 230V sockets available, it would be reasonable to expect them to be used to supply portable equipment outdoors.
However as they are not used for such, and they are not intended to be used by ordinary persons for general use, there is under the 17th edition no requirement to provide RCD protection.
 14 September 2012 12:30 PM
User is offline View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 17584
Joined: 23 March 2004

Originally posted by: spinlondon

The requirement is to provide RCD protection for: "mobile equipment with a current rating not exceeding 32 A for use outdoors."

Yup

The requirement could be met by use of an RCD plug.

For sure although I suppose there's a debate to be had whether a plug top falls under BS 7671 and therefore is the regulation focused on the circuit (ie source end RCD) and/or the outlet (RCD socket outlets)

However, that is not my point.

OK

The 16th requirement was directed at any socket which could reasonably be expected to be used for such a purpose.

Indeed

The 17th is directed at only such sockets that are actually used for such a purpose.

Well I guess you could argue any socket that could reasonably be forseen as supplying "mobile equipment with a current rating not exceeding 32 A for use outdoors."

Unless you have evidence that indicates a socket is actually being used to supply mobile equipment outdoors, there is no non-compliance.

Maybe Spin - I've taken a view on a recent job that plantroom sockets serving a plant room with external chilers and AHU's is likely to be used by maintenance staff - I argued with the contractor and we finally got the RCD sockets we specified originally - but it's subjective for sure - in this case I just happened to put up a better argument

Take for instance a couple of LU switch rooms that I recently worked on.

There are about nine DBs spread across the two rooms.

Each DB has had a single socket attached for the specific pupose of testing the Zs at each board.

As these are the only 230V sockets available, it would be reasonable to expect them to be used to supply portable equipment outdoors.

It would - hence my argument above - if they are only for Zs testing (where you don't want an RCD for obvious reasons) then a different pattern might have been best

However as they are not used for such, and they are not intended to be used by ordinary persons for general use, there is under the 17th edition no requirement to provide RCD protection.

Not really - the exception for skilled and instructed in (a) only relates to (i) not (ii) - in Reg 411.3.3


Regards

OMS

-------------------------
Failure is always an option
 14 September 2012 12:50 PM
User is offline View Users Profile Print this message


Avatar for spinlondon.
spinlondon

Posts: 4375
Joined: 10 December 2004

Of course really.
The sockets are not used to supply mobile equipment outdoors, so RCD protection is not required.
The sockets are not for use by ordinary persons, so RCD protection is not required.
The sockets are not intended for general use so RCD protection is not required.
The exception is not applicable, as no ordinary persons will use the sockets.
 14 September 2012 01:14 PM
User is offline View Users Profile Print this message


Avatar for OMS.
OMS

Posts: 17584
Joined: 23 March 2004

Originally posted by: spinlondon

Of course really.

The sockets are not used to supply mobile equipment outdoors, so RCD protection is not required.

I thought you said that they could predictably be used for that purpose - what does the Designers Risk Assessment say

The sockets are not for use by ordinary persons, so RCD protection is not required.

Agreed

The sockets are not intended for general use so RCD protection is not required.

OK - I guess they are labelled "For testing Purposes Only" or similar then

The exception is not applicable, as no ordinary persons will use the sockets.

Again, the exception in (a) and (b) only applies to (i) - if you suspect the sockets will supply mobile equipment outdoors then (ii) applies without the exception in (a) or (b)



Doesn't matter what it's intended for (ie a specific labelled etc outlet) or who uses it - if its used for mobile equipment outdoors (which you believe is entirely possible) there is no exception to (ii) so you need the RCD unless you also demonstrate an alternative to a circuit or socket RCD - ie an RCD plug top. As the designer you have no control over that - and as most mobile equipment doesn't come with an RCD plugtop then it's up to the designer, under his duties for CDM and from there to BS 7671 to provide it ?

Regards

OMS

-------------------------
Failure is always an option
 14 September 2012 01:16 PM
User is offline View Users Profile Print this message



John Peckham

Posts: 6880
Joined: 23 April 2005

No doubt these sockets for Zs testing would be suitably labeled then to comply with 411.3.3 (i) (b) to deter ordinary persons using them for general use or an extension lead plugged in to supply a power tool outside such as a jet wash used to clean the building fabric?

-------------------------
John Peckham

http://www.astutetechnicalservices.co.uk/
 14 September 2012 01:43 PM
User is offline View Users Profile Print this message


Avatar for spinlondon.
spinlondon

Posts: 4375
Joined: 10 December 2004

No I said it would be reasonable to expect them to be used for such.
But as that is no longer the criteria for providing RCD protection in the 17th, RCD protection is not required.
There is no requirement for the sockets to be labled.
That particular exception only applies to sockets that are intended for general use by ordinary persons.
Which part of the Regulations state 'if you suspect'?
Unless a socket is used to supply mobile equipment outdoors, there is no requirement for that socket to have RCD protection.
The 'reasonably expected' condition has been dropped.

OMS I am quite aware that there are no exceptions for skilled or instructed persons to the requirement to provide RCD protection for mobile equipment used outdoors.
I have not at any time suggested that there is.
Why you keep banging on about it as if I have is a bit mystifying?
The requirement to provide RCD protection for mobile equipment used outdoors, does not specify socket-outlets, nor does it mention 'reasonably expected', 'suspicions', 'what might happen' or any other perhaps or maybe.
It is quite specific, mobile equipment used outdoors must be provided with RCD protection
If no mobile equipment is used outdoors, there is no requirement to provide RCD protection.
 14 September 2012 02:00 PM
User is offline View Users Profile Print this message



John Peckham

Posts: 6880
Joined: 23 April 2005

Spin

"If no mobile equipment is used outdoors, there is no requirement to provide RCD protection."

How do you know that then?

-------------------------
John Peckham

http://www.astutetechnicalservices.co.uk/