Topic Summary: Oven with a 12.17amp loading
Created On: 07 December 2017 06:17 PM
Status: Read Only
Linear : Threading : Single : Branch
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 07 December 2017 06:17 PM
User is offline View Users Profile Print this message



nige296

Posts: 89
Joined: 04 December 2009

Supplying a cooker isolation switch (with a socket outlet) via a 20amp RCBO with a 6mm2 T&E clipped direct. (future proof cable)

The oven is only a 12.17amp load. (Gas hob)

Is the 20amp RCBO OK for the oven or is this to high for the oven?

or do I need to fuse down the oven to 13amps

Don't really want to use a 16amp RCBO as the outlet may be used for a kettle as well!

Thanks for any thoughts
 07 December 2017 06:21 PM
User is offline View Users Profile Print this message



daveparry1

Posts: 7749
Joined: 04 July 2007

That will be fine Nige, as also would a 32 amp mcb. The mcb is there to protect the cable not the appliance.
 07 December 2017 07:11 PM
User is offline View Users Profile Print this message



AJJewsbury

Posts: 16095
Joined: 13 August 2003

Provided it meets the oven manufacturer's instructions (some specify a maximum fuse/MCB rating) then all's well.
- Andy.