Topic Title: Electrical distribution on fire escape
Topic Summary:
Created On: 17 July 2017 09:06 AM
Status: Read Only
Linear : Threading : Single : Branch
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 17 July 2017 09:06 AM
User is offline View Users Profile Print this message



GR1981

Posts: 11
Joined: 29 February 2016

Hi All

Hoping someone will be able to help.

We're currently working on an office refurb and looking the move the electric meter and cut-out. The supply is around 70kVA.

We're looking to move it to a circulation space and I have been looking to see what current regs say regarding electric supplies being on escape routes.

I thought there might be something in Approved Document B but I couldn't see anything. Is it something that should be picked up in the FRA?

I welcome your thoughts!
 17 July 2017 09:23 AM
User is offline View Users Profile Print this message



di515223

Posts: 337
Joined: 08 July 2010

A bit more information required.
Is the intention to have the equipment exposed in the circulation area? (Unlikely I would suspect)
If not, how is it to be enclosed and what fire rating is the enclosure going to have? - Even 2 layers of Plasterboard changes the fire spread characterisitcs.
If this is a fire escape, how high?
This needs a lot of input from many people before you go ahead. I assume you are working with all the relevant parties to plan this as there are many things (some not obvious) to take into account. I would avoid this if possible, as the requirements will be much more onerous than in a properly designed plant room.
I may seem a stupid question, but where is this? The regulations vary between Engalnd, Scotland, Wales and Northern Ireland.

Dave
 17 July 2017 09:49 AM
User is offline View Users Profile Print this message



GR1981

Posts: 11
Joined: 29 February 2016

Hi Dave

apologies for the lack of details.

The equipment would have to have some form of enclosure in to prevent interference by anyone that passes. As I was just looking into the feasibility of moving it to this location, the fire rating of the enclosure hasn't been discussed. I would imagine it would have to be a 60 minute fire rating if it was allowed to be installed in the proposed location.

This area forms the landing between stairwells, with the space measuring around 2500mm x 1800mm, and both stairwells being at the same end of this area.

And I should've said that this was in England.

I posted this question to see if it was a no-go before I submitted the application to UKPN for a service alteration. Also, if it was a non-starter I could go back to the architect to start discussing alternative solutions. I'm working with the design team as well as the DNO but in terms of the less obvious things to take into account, I would welcome any advice.

Thanks!
 17 July 2017 10:38 AM
User is offline View Users Profile Print this message



alancapon

Posts: 6814
Joined: 27 December 2005

You need to ask UKPN. We would say on a solid wall, within 1.5m of an external door.

Regards,

Alan.
 17 July 2017 11:51 AM
User is offline View Users Profile Print this message



GR1981

Posts: 11
Joined: 29 February 2016

Thanks for the reply Alan.

I've put the application in but I suspect it'll be knocked back, so we're working on alternative solutions.

Thanks
 17 July 2017 12:06 PM
User is offline View Users Profile Print this message



alancapon

Posts: 6814
Joined: 27 December 2005

Other suggestions are an outside meter box, or a suitably sized cupboard built into / against a wall outside the building. I can think of several instances where a brick or blockwork cupboard has been constructed.

Regards,

Alan.
 17 July 2017 08:56 PM
User is offline View Users Profile Print this message



Timeserved

Posts: 65
Joined: 18 October 2016

Can someone tell me what UKPN stands for? I'm guessing UK Power Network provider? am I far off? Thanks.
 17 July 2017 10:10 PM
User is offline View Users Profile Print this message



typiod

Posts: 481
Joined: 09 February 2008

UK Power Networks. Owned by the Chinese (Hong Kong).
 17 July 2017 11:13 PM
User is online View Users Profile Print this message



OMS

Posts: 22284
Joined: 23 March 2004

Originally posted by: typiod

UK Power Networks. Owned by the Chinese (Hong Kong).


AKA - Sweet 'n Sour Light 'n Power

OMS

-------------------------
Let the wind blow you, across a big floor.
 18 July 2017 12:17 PM
User is offline View Users Profile Print this message



GR1981

Posts: 11
Joined: 29 February 2016

Originally posted by: OMS

Originally posted by: typiod



UK Power Networks. Owned by the Chinese (Hong Kong).




AKA - Sweet 'n Sour Light 'n Power



OMS


OMS I love that. I'm going to have to call them sweet 'n sour from now on.

Spoke to sweet 'n' sour and they are going to come out to site to see what the options are.
 19 July 2017 12:34 PM
User is offline View Users Profile Print this message



MHK

Posts: 24
Joined: 29 July 2011

Originally posted by: OMS
AKA - Sweet 'n Sour Light 'n Power
OMS


LOL that's made my day