what test(s) should be carried on a newly constructed low voltage to test for its effectiveness?
 28 June 2010 04:56 PM
User is offline View Users Profile Print this message



tope4rilly2k

Posts: 12
Joined: 30 November 2009

I am young project engineer.its for industrial application.a company is assembling some electrical panels(80A-250A-current rating) for me and i intend testing them before they are been delivered to me
 28 June 2010 05:57 PM
User is offline View Users Profile Print this message



OMS

Posts: 22428
Joined: 23 March 2004

Contractually, you may be better advised to get the manufacturer to test them whilst you witness those tests.

For "normal use" you might want to consider the following:

Visual examination of the exterior

Visual Examination of the interior

Torque testing of manufactured joints

"Ductor" Continuity tests

Insulation Resistance tests

Current injection testing

Functional operation checks

Regards

OMS

-------------------------