what test(s) should be carried on a newly constructed low voltage to test for its effectiveness?
|
|
|
|
|
|
|
|
|
I am young project engineer.its for industrial application.a company is assembling some electrical panels(80A-250A-current rating) for me and i intend testing them before they are been delivered to me
|
|
|
|
|
|
|
|
|
Contractually, you may be better advised to get the manufacturer to test them whilst you witness those tests.
For "normal use" you might want to consider the following: Visual examination of the exterior Visual Examination of the interior Torque testing of manufactured joints "Ductor" Continuity tests Insulation Resistance tests Current injection testing Functional operation checks Regards OMS ------------------------- Failure is always an option |
|
|
|
|
|