IET
Decrease font size
Increase font size
Topic Title: Earthing Conductor
Topic Summary:
Created On: 07 March 2014 09:42 AM
Status: Read Only
Linear : Threading : Single : Branch
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
User is offline View Users Profile Print this message
jackdaniel
With reference to IEEE 80 and BS7430, there is an equation to determine the size of earthing conductor for substation grounding which is s2=i2t/k2 , This earthing conductor sizing is referred to transformer neutral ground or any other equipment?
 07 March 2014 02:51 PM
irevans
Not sure I understand what you are asking. BS 7430 defines an earthing conductor as a "protective conductor connecting the main earthing terminal of an installation to an earth electrode or to other means of earthing"; i.e. it is not a neutral conductor, which is separately defined.
irevans
IET » Energy » Earthing Conductor
Statistics
See Also: