What is the sensitivity setting for arc welding machine for current rating 100A, 3P. I don't think 30mA is suitable.
 04 March 2014 12:49 PM
AdrianWint
Why do you feel that such a machine even needs earth leakage protection?
 04 March 2014 01:22 PM
The supply to the welding set may require RCD protection depending on how it is connected, and where it is used.
For a large, static set, RCD protection isn't a specific requirement, but if you expect it to prove additional protection for users, then only a 30mA device is applicable. You could have a higher triping value if you want protection say from fire or similar. That said, a 100mA or 300mA device will still offer a lot of protection to users.
An RCD won't be of any use to prevent shocks on the workpiece side of the welder - you need proper procedures and use of PPE for that.