Topic Title: storage of transformer
Topic Summary: Outdoor storage
Created On: 11 October 2013 08:06 AM
vvvviswavijay
Hi Engineers,
I read this extract from a transformer manufacturer manual.
" Transformers which are required to be kept in storage for long periods should be preferably be drained of oil and the tanks should be filled wit h dry nitrogen gas under slight pressure"
Request you t ogive your valuable suggestions. Is this method appropriate or not advisable to follow?
Thanks in advance.
Vj
 11 October 2013 09:44 AM
Zuiko
Follow the manufacturer's recommendations.
The rationale is to avoid moisture ingress contaminating the oil which leads to all sorts of problems.
 12 October 2013 10:12 AM
statter
... normally the iron losses mean they are slightly warm even when off load in operation which helps keep moisture at bay. In storage you don't have this and natural temp changes will gradually introduce moisture which will be absorbed by the oil.....
 12 October 2013 03:20 PM
tariqahmadani
Yes. The instructions are correct for storage. Normally the oil is drained to avoid ingress of moisture in it while not in operation. Nitrogen is a dry gas and helps keep moisture out of transformer.
 24 October 2013 04:27 AM
vvvviswavijay
Thank you zuiko
 24 October 2013 04:30 AM
vvvviswavijay
Thank you statter
I to agree with your comments, zuiko and tariqahmadani.
Appreciate your time and suggestions.
Best Regards
Vj
IET » Energy » storage of transformer