Hi Engineers,

I read this extract from a transformer manufacturer manual.

" Transformers which are required to be kept in storage for long periods should be preferably be drained of oil and the tanks should be filled wit h dry nitrogen gas under slight pressure"

Request you t ogive your valuable suggestions. Is this method appropriate or not advisable to follow?

Thanks in advance.

Regards
Vj

 11 October 2013 09:44 AM
User is offline View Users Profile Print this message



Zuiko

Posts: 521
Joined: 14 September 2010

Follow the manufacturer's recommendations.

The rationale is to avoid moisture ingress contaminating the oil which leads to all sorts of problems.
 12 October 2013 10:12 AM
User is offline View Users Profile Print this message



statter

Posts: 126
Joined: 06 February 2013

... normally the iron losses mean they are slightly warm even when off load in operation which helps keep moisture at bay. In storage you don't have this and natural temp changes will gradually introduce moisture which will be absorbed by the oil.....
 12 October 2013 03:20 PM
User is offline View Users Profile Print this message


Avatar for tariqahmadani.
tariqahmadani

Posts: 3
Joined: 10 November 2009

Yes. The instructions are correct for storage. Normally the oil is drained to avoid ingress of moisture in it while not in operation. Nitrogen is a dry gas and helps keep moisture out of transformer.
 24 October 2013 04:27 AM
User is offline View Users Profile Print this message



vvvviswavijay

Posts: 39
Joined: 11 September 2003

Thank you zuiko
 24 October 2013 04:30 AM
User is offline View Users Profile Print this message



vvvviswavijay

Posts: 39
Joined: 11 September 2003

Thank you statter

I to agree with your comments, zuiko and tariqahmadani.

Appreciate your time and suggestions.

Best Regards
Vj
IET » Energy » storage of transformer

Topic Tools Topic Tools
Statistics

See Also:



FuseTalk Standard Edition v3.2 - © 1999-2015 FuseTalk Inc. All rights reserved.