Topic Title: Transformer Impedance Test & X/R Ratio
Created On: 25 July 2013 09:14 AM
Where is my avatar image?
jackdaniel
So guys, please help me to verify my calculation,
From the short circuit Test of 4 kVA, 400/200 V, 50 Hz, 3-phase transformer has the following test data
SC test: 20V, 10A, 100W
Impedance % = (20/400) *100 = 5%
Z= V/I = 20/10 = 2 Ohm
R = P/3*I*1 = 100/(3*10*10) = 0.333 Ohm
X = SQRT(Z2 - R2) = 1.972 Ohm
So X/R ratio of the transformer is 1.972/0.333 = 5.922.
is it correct?
 25 July 2013 10:01 PM
JonathanHill
I may be getting a bit rusty, my recollection for sc testing is to short-circuit the secondary (assume the 200V windings) and then raise the voltage until full load current flows in the primary.
I get the primary FLC to be 5.797A which differs from your value. So unless my methodology is wrong, you can't deduce the impedance or X/R ratio from these test results.
Looking forward to hearing from others.
Jonno
 28 July 2013 04:12 PM
jackdaniel
John,
Act I pick randomly the value, my objective is to determine the X/R value from the test.
 29 July 2013 12:01 AM
JonathanHill
Apart from the SC issue and values, I think your approach was OK, but would appreciate a sanity check from others.
Jonno
 11 August 2013 06:40 PM
sreeraasi94
Correct!