On say a UK installed transformer 1000KVA 11kV/433V I see why we would need a rating above 400V to address volt drop but why the magic figure of 433V?
 19 July 2013 11:50 AM
User is offline View Users Profile Print this message



Spen008

Posts: 3
Joined: 09 July 2013

433V is the no load votlage at the transformer secondary terminals. It is industry practice to quote the no load voltage. When a load is connected there will be voltage drop within the transformer windings.
 19 July 2013 04:22 PM
User is offline View Users Profile Print this message



MickeyB

Posts: 181
Joined: 18 January 2003

415V was the nominal voltage on full load...... 433V is the no load voltage which allows for 18V internal volt drop....
The % impedance or 'voltage impedance' of the transformer is related to the internal voltage drop.... therefore a 4% transformer would typically have a 4% internal volt drop or 18V. Overall it was 10% volt drop from source to final circuit..... 6% max at source, 4% in the sub-mains/ final circuit.

Distribution transformer typically had internal impedance rating of between 4~6%.