IET
Decrease font size
Increase font size
Topic Title: Voltage Test Terminal & Current Test Terminal in Switchgear
Topic Summary:
Created On: 08 March 2013 02:47 AM
Status: Post and Reply
Linear : Threading : Single : Branch
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 08 March 2013 02:47 AM
User is offline View Users Profile Print this message



jackdaniel

Posts: 19
Joined: 29 November 2012

what are the Voltage Test Terminal & Current Test Terminal, and wht is the test terminal block
 08 March 2013 08:06 PM
User is offline View Users Profile Print this message


Avatar for slittle.
slittle

Posts: 3080
Joined: 22 November 2007

It sounds to me like we are doing your college assignment question by question.

On a CT metering enclosure, there is normally a test terminal block provided on the front (or sometimes inside the first door). The terminal names pretty much speak for themselves.


Stu
 08 March 2013 10:39 PM
User is offline View Users Profile Print this message



dlane

Posts: 646
Joined: 28 September 2007

I have come across din rail mounted test terminals or panel mounted test blocks such as the Midos system.

VT test terminals are standard terminals allowing you to measure the VT voltage, they may have adapters for 4mm test plugs built into them.

The CT test terminals allow you to connect in series with the CT circuit to measure the current, they short out automatically when the meter is disconnected to maintain the circuit.

Some din rail systems I have come across involved links that could be moved manually to short out the CT or connect a meter into the circuit.

Kind regards

Donald Lane
Statistics

See Also:



FuseTalk Standard Edition v3.2 - © 1999-2013 FuseTalk Inc. All rights reserved.