Topic Title: Medium Switchger CT
Created On: 05 March 2013 01:52 AM
jackdaniel
How many CT for medium Switchgear per phase?, please describe the function for each CT?
 05 March 2013 10:12 AM
The number of CTs per phases will depend on the protection design for that particular circuit breaker, as well as whether busbar protection is required for the board. It will also depend on the company policy for sharing CTs.
Edited: 05 March 2013 at 11:34 AM by alancapon
 06 March 2013 12:49 AM
jackdaniel
It is possible to share the CT for overcurrent protection and earth fault protection?
 06 March 2013 08:48 PM
cookers
yes if you use a combined overcurrent and earth fault protection relay it normal practice.
http://www05.abb.com/global/sc...PAJ140C%20Brochure.pdf
 07 March 2013 12:13 AM
jackdaniel
Nope, they use separate CT for this model, i hv seen this model by myself, as you can see from the drawing,
Anyway, thanks for ur info,
 07 March 2013 08:41 AM
As I said, it depends on the protection design and operating company policy. It would also be possible by altering the connections to the relay to achieve the same arrangement using only the three phase CTs and not use a separate one for earth. You need to ensure that you order the correct specification CTs for your protection application. It would be possible (but most companys would think unwise) to use the same CTs for backup overcurrent / earth fault as well as a high speed protection scheme such as unit and / or accelerated distance as well.
Regrads,
 07 March 2013 09:43 PM
dlane
We utilise both types of setup on our protection systems.
Generally our HV transformer feeders utilise the phase CTs for earth protection.
Our HV incomers and LV incomers generally have seperate CTs for phase and earth protection circuits and a further CT for restricted earth fault protection for transformer secondaries.
Kind regards
Donald Lane
 08 March 2013 01:03 AM
In terms of the greatest number of phase CTs, I think we have got to five sets of CTs. For a transmission feeder, these would be:
1. First Main Protection (Usually a unit scheme)
2. Second Main Protection (Usually an accelerated distance scheme)
3. Overcurrent / Earth Fault / Sensitive Earth Fault
4. Busbar Protection Zone (a high-impedance scheme)
5. Busbar Protection Check Zone (a high-impedance scheme)