Hi All,
Could anyone explain how these balancers work please? many thanks |
|
|
|
|
|
|
|
|
Hello,
I think (though probably wrong) they are just a small TX with slightly more windings on one side than the other or possible a tap changer so as the output voltage can be adjusted on-site. As far as I'm aware they can only increase volts not amps so will only be used on long runs where volt-drop is an issue but load isn't. What I would say is if you find any information online about them I'd be very great full, as we've got a few on our network, and very little information is available on them. Hope this is any use to you. Edited: 01 March 2013 at 06:32 PM by Snips |
|
|
|
|
|
|
|
|
There are two things you could be taliking about. The first is a "regulator", which is a three-phase 1:1 ratio transformer with a tap changer and a basic voltage control relay, these are used to compensate for long overhead lines. The second is a "static balancer" which has two sets of windings connected in zig-zag, which effectively re-positions the neutral such that all phase to neutral voltages are equal.
The "static balancer" is usually placed at the end of a line, whereas the "regulator" is placed along it. The "static balancer" also usually has a fuse in its neutral connection. If a phase is shorted to the neutral due to a fault, the balancer may draw a significant current, which can be large enough to "burn down" the remaining phases. This should be prevented by the balancer's neutral fuse operating. Regards, Alan. |
|
|
|
|
|
IET
» Energy
»
Low voltage pole mounted balancers
|
Topic Tools |
FuseTalk Standard Edition v3.2 - © 1999-2013 FuseTalk Inc. All rights reserved.