Good morning folks i wondered if any one could perhaps recommend a product to help with an 'over voltage' problem i have frrm time to time.
The senario is that we have some 20ft containers containing a breathing air compressor which we send out to remote locations for breathing apparatus and gas detection support. The trouble is that from time to time the customers on-site generator (we suspect) is giving out a little more voltage than intended and is destroying any voltage sensitve equipment pluged into the socket outlets. I am thinking that an inline unit which can be wired in between the main isolator and distribution panel might be the answer. Normal 3 phase voltage on site - 400V 50Hz Max load 63 Amp Any suggestions or reccomendations would be much appreciated! |
|
|
|
|
|
|
|
|
hello,
firstly you need to know abit more before just fitting a unit to cure this problem. If the problems are due to overvoltages lasting anything over a few seconds, then a surge/transient protector unit will not work in the way intended. Surge/transient protectors should only be used to protect against very short duration events in the millisecond duration's. A sustained overvoltage will kill a surge/transient suppressor unit. If you are just getting spike/surges then a Surge protection unit will cure these problems. You could fit a unit like the Furse ESP415M1 or ESP415D1, both of these units will protect sensitive electronics very well as they will only let through 600V at a time of surge/transient voltage. Hope this is of some help. |
|
|
|
|
|
|
|
|
Hi Nick,
Thankyou very much for the advice i will have a look a the manufacturers data sheets. Unfortunatly we do not have the opportunity to do any kind of site survey on the electrical supply, my hunch is that the problem is spike/surge related and not a sustained overvoltage as only the most sensative if equipment appears to be effected. All other electrical equipment and wiring is unaffected. Best Regards & Many Thanks Alan |
|
|
|
|
|
|
|
|
From what you have said in the reply it sound most likely that you are getting spike/surge related problems. The sensitive electronics equipment will be protected by the units I have mentioned above.
Hope you get to the bottom of your problem. |
|
|
|
|
|