Topic Title: Unbalanced voltage in an induction motor
Topic Summary: Symmetrical components results
Created On: 06 December 2012 08:43 PM
Status: Read Only
Linear : Threading : Single : Branch
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 06 December 2012 08:43 PM
User is offline View Users Profile Print this message



leeeggy

Posts: 8
Joined: 20 November 2011

I have a problem on a customers site with an imbalance in the LV phases from the supply. One phase is about 5% down on the other 2 so its causing excessive currents in the 110kW motor. I understand its to do with the negative phase component and proceeded to calculate the positive and negative components and then the negative current but i'm not sure if i'm getting the right answer, which i understyand to be somewhere in the region of 6-7 time FLC. My customer is pushing for a report he can then pass to the supply authority to prove the tripping problem is related to their supply. Any technical geeks who can point me in the right direction.
Cheers
 06 December 2012 11:51 PM
User is offline View Users Profile Print this message


Avatar for sfchew.
sfchew

Posts: 589
Joined: 10 December 2002

Please provide line voltages and currents when motor is running. What protection relay has tripped and the relay settings?

Regards
Chris Chew
 07 December 2012 07:56 AM
User is offline View Users Profile Print this message



leeeggy

Posts: 8
Joined: 20 November 2011

the line voltages are:
r-y 439
y-b 417
b-r 439
the currents when checked during loading were:
r-220a
y-180a
b-150a
The currents when checked off load were:
r-85a
y-70a
b-66a
 07 December 2012 08:02 AM
User is offline View Users Profile Print this message



leeeggy

Posts: 8
Joined: 20 November 2011

and the trip device is a combined overload and thermal circuit breaker molded case part number schneider electric GV7RE220
cheers
 07 December 2012 09:55 AM
User is offline View Users Profile Print this message



leeeggy

Posts: 8
Joined: 20 November 2011

I did calculate the negative sequence component to be 200a which is near enough FLC but i don't know if its right
 07 December 2012 03:45 PM
User is offline View Users Profile Print this message


Avatar for sfchew.
sfchew

Posts: 589
Joined: 10 December 2002

Please give the relay setting.

Regards
Chris Chew
 07 December 2012 04:19 PM
User is offline View Users Profile Print this message


Avatar for aroscoe.
aroscoe

Posts: 91
Joined: 18 October 2002

Hmm. My gut feel was that you have >2% unbalanced voltages, but actually this may not be so.

The following MATLAB code, assuming that the voltages are still 120 degrees apart, shows that the actual unbalance (based on negative sequence) is only 1.69%, so technically this is still within EN50160 limits of 2%, and the utility isn't bound to do anything about it. But, clearly, this is not desirable!

a = exp(j*pi*2/3)
a2 = exp(-j*pi*2/3)
abc_to_PosNegZero = 1/3 * [ 1 a a2 ; 1 a2 a ; 1 1 1 ]
PosNegZero_to_abc = inv(abc_to_PosNegZero)


p1 = 1*exp(j*0)
p2 = conj(a)
p3 = conj(a2)

% Example customer premesis measurements

Vabc = [439*p1 417*p2 439*p3].'

PosNegZero = abc_to_PosNegZero*Vabc

Unbalance_pct = abs(PosNegZero(2))/abs(PosNegZero(1))*100

Unbalance_pct =

1.6988

-------------------------
Dr. Andrew Roscoe

http://personal.strath.ac.uk/andrew.j.roscoe
 08 December 2012 08:31 AM
User is offline View Users Profile Print this message



leeeggy

Posts: 8
Joined: 20 November 2011

Overload is set at 110% FLC so 210a
 08 December 2012 10:59 AM
User is offline View Users Profile Print this message


Avatar for sfchew.
sfchew

Posts: 589
Joined: 10 December 2002

What is the load profile of the motor? Is the load constant or changing according to its burden? It is quite obvious that the relay setting is too low for the motor operation. Is there any means of monitoring the motor temperature?

Regards
Chris Chew
 08 December 2012 12:27 PM
User is offline View Users Profile Print this message



leeeggy

Posts: 8
Joined: 20 November 2011

Andrew,
Those voltages were taken during off load periods, once the mixer is loaded then the voltages drop but the difference remains the same.
Loading voltages:
r-y 419
y-b 399
b-r 419
Also if it is proven to be more than 2% imbalanced then do the supply authority just need to improve to better than 2% ie:1.99%, which won't improve the situation. If this is the case then we'll need a generator set.

Cheers
Doc
 08 December 2012 12:32 PM
User is offline View Users Profile Print this message



leeeggy

Posts: 8
Joined: 20 November 2011

the mixer load profile is as almost S6 type loading, with continuous running and intermittent loading to full capacity then steady off loading before starting the cycle again. i have another plant doing exactly the same work but with a balanced supply and the current loading there doesn't trip the mixer at all.

Cheers
 09 December 2012 02:35 AM
User is offline View Users Profile Print this message


Avatar for sfchew.
sfchew

Posts: 589
Joined: 10 December 2002

The report based on the voltage and currents recorded will provide a good basis for the utility to rectify the voltage unbalance. The motor trippings need to be emphasized so that they can regard this case as urgent because of loss of production.

Regards
Chris Chew
 09 December 2012 08:37 PM
User is offline View Users Profile Print this message



leeeggy

Posts: 8
Joined: 20 November 2011

thanks Chris, I'll push the customer to get this rectified based on what I've done so far. As it happens, my customers energy supplier is the also their customer but i think they are dragging their heels hoping the problem will just go away but if anything its getting worse. I'm going to site on Tuesday so hopefully is can meet with who ever and iron this one out.