Hi guys,

How to size the breaker for the primary transformer beside the normal formula?, i believe there are several factor to be considered beside the input current based on I=KVA/(1.732*V)
 30 November 2012 05:31 AM
User is offline View Users Profile Print this message



thamee97

Posts: 14
Joined: 13 February 2003

Hi,

Important aspects are short-circuit interrupting rating (symmetrical/asymmetrical) and short-circuit withstand ratings (including duration). Fault levels shall be evaluated at the point of breaker location to define these requirements.

Regards,
 30 November 2012 06:06 AM
User is offline View Users Profile Print this message



jackdaniel

Posts: 69
Joined: 29 November 2012

How about another factor in determine the nominal current?..such as inruah current factor?