Topic Title: Transformer
Topic Summary: Anyone knows anything the pressure PSI ?
Created On: 15 July 2012 01:37 AM
Status: Read Only
Linear : Threading : Single : Branch
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 15 July 2012 01:37 AM
User is offline View Users Profile Print this message



Linspire

Posts: 30
Joined: 07 June 2010

Hi,

How am I going to know whether the transformer tank can withstand of pressure 10PSI instead 8PSI ?

The calculation only involved bending stress and deflection ?
Sorry, I'm new to this problem.



Regards
Linspire
 15 July 2012 10:12 AM
User is offline View Users Profile Print this message



ArthurHall

Posts: 735
Joined: 25 July 2008

We need more information. What size of transformer, which fluid, why the increase in presure?
 15 July 2012 10:22 AM
User is offline View Users Profile Print this message



Linspire

Posts: 30
Joined: 07 June 2010

Sorry, I mean customer requires 10PSI normally, but the supplier provides 8PSI model.

Did request calculation to proof 8PSI is sufficient enough, however only received calculation of bending stress values & deflection values. Does this two calculation mean anything ?
 15 July 2012 12:32 PM
User is offline View Users Profile Print this message



Jaymack

Posts: 4586
Joined: 07 April 2004

They probably can't answer the question, but I would get the supplier's confirmation in writing, for any proposed deviance to their technical specification, or applicable standard of manufacture. It's all about calculation, design and type/proof testing. Obviously related to "bending stress values & deflection values".

Regards
 15 July 2012 01:28 PM
User is offline View Users Profile Print this message



Linspire

Posts: 30
Joined: 07 June 2010

Ok, thank you very much Jaymack.
 15 July 2012 02:40 PM
User is offline View Users Profile Print this message



alancapon

Posts: 5745
Joined: 27 December 2005

Originally posted by: Linspire
Sorry, I mean customer requires 10PSI normally, but the supplier provides 8PSI model.

Did request calculation to proof 8PSI is sufficient enough, however only received calculation of bending stress values & deflection values. Does this two calculation mean anything ?

What does the customer say?

If I received a transformer pressurised at 8psi instead of the 10psi I had specified, or pressurised at 10psi when the manufacturers documentation said 8psi, either the transformer would not be staying on site for long, or the commissioning (and therefore final payments) would not be happening. I would expect a document requesting the change, backed up by the manufacturers documentation where relevant!

Regards,

Alan.
 15 July 2012 04:11 PM
User is offline View Users Profile Print this message



Linspire

Posts: 30
Joined: 07 June 2010

alancapon,

Actually I plan do as what you suggested, before I do so, I need to find out what/why/how these calculation they provided.
I even read through IEC paper (600289) which does not specify the pressure ? Haha..well, first time gone through this problem.

Thank you alancapon for you suggestion.
 15 July 2012 04:52 PM
User is offline View Users Profile Print this message



alancapon

Posts: 5745
Joined: 27 December 2005

For this transformer, what is:
- the voltage ratio
- the power rating
- the insulating medium
- what is the tank pressurised with?

Regards,

Alan.
 15 July 2012 11:36 PM
User is offline View Users Profile Print this message



Linspire

Posts: 30
Joined: 07 June 2010

Originally posted by: alancapon

For this transformer, what is:

- the voltage ratio

- the power rating

- the insulating medium

- what is the tank pressurised with?



Regards,



Alan.



Hmm..may I know how'd those information link to ?