Topic Title: Induced voltage in control cables, that holds the relay energized.
Topic Summary: Long run control cable (Okanite, cu, approx 600m) parallel run with LV cables in aluminum cable tray
Created On: 09 June 2012 03:34 PM
Status: Post and Reply
Linear : Threading : Single : Branch
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 09 June 2012 03:34 PM
User is offline View Users Profile Print this message



jagansarah

Posts: 11
Joined: 26 September 2008

Scenario:
In a Construction industry,

Long run control cable induces approx 33 vac voltage at (magnetic contactor coil) medium voltage control panel (120volt, ac control voltage).

It causes, the magnetic relay negating stop command, and holds the contactor energised.

The length of the metal clad cable over 600 m and runs along with other Low Voltage Cu. cables in aluminium cable tray, cable tray & supports are bonded at both end with a stable grid grounding system.

To drain the residual (induced) voltage in the control cable, we put wire wound resistor (10W, 20K), parallel to (circuit) the magnetic contactor coil. It works well so far, and found one resistor is burnt among the group(s).

Is there any other recommended solution to resolve this issue, such as RC circuit, and how to calculate.

please advice, and thanks in advance.

Edited: 11 June 2012 at 08:21 AM by jagansarah
 10 June 2012 07:14 PM
User is offline View Users Profile Print this message


Avatar for JonathanHill.
JonathanHill

Posts: 204
Joined: 09 September 2002

Alstom Grid make a dc control relay (type MVAW) designed for long pilot wire applications, which has a high rejection of induced ac voltages

It would be interesting to know what the residual voltage is with the resistors connected, and also what your control voltage is.

Jonno

-------------------------
Jonno
 11 June 2012 08:40 AM
User is offline View Users Profile Print this message



jagansarah

Posts: 11
Joined: 26 September 2008

Thank you for your response. (Note: resistor connected parallel, not series, typo error)
Control voltage: 120 vac, 60hz
voltage across the M-IV contactor coil, 33vac,
after installing the shunt resistor : zero voltage measured arcoss the coil.