 31 May 2012 05:19 AM
User is offline View Users Profile Print this message


Avatar for adieboy.
adieboy

Posts: 1
Joined: 06 September 2011

Hi,

What is the BDV test of the 11kV oil RMU?

Also, is there a standard, specifying the preferable value of this test?

Regards,

Edited: 31 May 2012 at 11:26 AM by adieboy
 04 June 2012 01:15 PM
User is offline View Users Profile Print this message


Avatar for jagansarah.
jagansarah

Posts: 11
Joined: 26 September 2008

The dielectric strength of new insulating oil shall be measured in accordance with the following ASTM testing methods:

a. ASTM D877, "Test Method for Dielectric Breakdown Voltage of Insulating Liquids using Disk Electrodes (30 KV minimum)"

b. ASTM D1816, "Test Method for Dielectric Breakdown Voltage of Insulating Oils from Petroleum Origin Using VDE Electrodes ~0.04 inch, (28 kV minimum)"