Topic Title: Breakdown Voltage Test (BDV) of 11kV Oil Ring Mian Unit (RMU) Topic Summary: Created On: 31 May 2012 05:19 AM Status: Post and Reply |
Linear : Threading : Single : Branch |
Search Topic |
Topic Tools
|
|
|
|
|
Hi,
What is the BDV test of the 11kV oil RMU? Also, is there a standard, specifying the preferable value of this test? Regards, Edited: 31 May 2012 at 11:26 AM by adieboy |
|
|
|
|
|
|
|
|
The dielectric strength of new insulating oil shall be measured in accordance with the following ASTM testing methods:
a. ASTM D877, "Test Method for Dielectric Breakdown Voltage of Insulating Liquids using Disk Electrodes (30 KV minimum)" b. ASTM D1816, "Test Method for Dielectric Breakdown Voltage of Insulating Oils from Petroleum Origin Using VDE Electrodes ~0.04 inch, (28 kV minimum)" |
|
|
|
|
|