What are the IEC standards covering the design of EHV cables?
I have the requirements for Testing, but not manufacture.
Should the conductor have a metalic tape/wire screen around it, like MV cables?
I have come across some cable from Korea with a corrigated alumimum sheath, but no conductor metailic screen!

Is this cable to IEC standard??
 28 May 2012 04:01 PM
User is offline View Users Profile Print this message



irevans

Posts: 181
Joined: 07 March 2002

Assuming you are talking XLPE, the IEC standard is IEC 62067. Unlike lower down the voltages the cable design is not dictated. A metallic conductor screen is not required. The manufacturer details should identify if this meets the IEC standard.

-------------------------
irevans
 29 May 2012 03:34 AM
User is offline View Users Profile Print this message



bobramsey

Posts: 26
Joined: 17 December 2003

Hi irevans

Yes it is XLPE cable and the standard I have is IEC 62067 - which the manufacture claims it is produced to and is stated in the data/spec sheet for the cable.