I wonder if anyone can help me
I am trying to obtain generic errors for a metering 33Kv metering VT to satisfy the meter operator. The original errors have been mislaid by the manufacturers and I require a copy of typical errors for a similar VT Details are below:- Manufacturer = AEG Type EY36TAW1 Burden 60Va Class 0.5 to IEC standard 186 Ratio 33000/110V If someone can help with this query than that would be great Thanks and Merry Xmas all Viv. |
|
|
|
|
|
|
|
|
A class 0.5 VT should have the voltage within +/- 1% and the phase within +/- 40'
|
|
|
|
|
|
|
|
|
My Areva NPAG manual gives a class 0.5 VT as +/- 0.5% accuracy with a +/- 20 minute displacement for a burden of between 0.25 and 1.0 at 0.8pf.
I believe IEC 60044 is the series for instrumentation transformers with part 2 being for inductive voltage transformers and part 5 for capacitive voltage transformers Kind regards Donald Lane |
|
|
|
|
|
|
|
|
Thanks Arthur
Merry Xmas |
|
|
|
|
|
|
|
|
Many thanks Donald
Merry Xmas Viv |
|
|
|
|
|