Hi,

Did some current measurements on a main supply today L1 - 82A, L2 - 99A, L3 - 63A. Any ideas on how to get these balanced out. I know how, just want some more input on the matter and if any new ideas/ products/ suggestions crop up........
Thanx
 09 October 2009 09:50 PM
User is offline View Users Profile Print this message



ernairnp

Posts: 260
Joined: 05 August 2003

Mr. Ablelectrical,

I assume that yours is a three phase FOUR WIRE system.

You will have to take a large number of readings for various times of the day and week. Then physical changes of loads from one phase to another, based on your judgement, alone is the solution.

You will not be able to have perfect phase balance always. But by proper selection, you can minimise the unbalances for various times.

-------------------------
Best wishes & regards
N P NAIR, MSc (Engg), C Eng, FIE(I), MIEE,Sr MIEEE.
 09 October 2009 11:43 PM
User is offline View Users Profile Print this message



sh3749

Posts: 8
Joined: 30 April 2003

Balancing depends entirely on the configuration of loads connected to each. I assume that the connected loads are mostly SP+N so if this is an existing installation it would be difficult taking the point raised bye rnairnp to determine whether there was an actual imbalance or just that the loads were being used at varying times creating a perceived imbalance.

If you can list all the loads and their current values and can change which phase they are connected to then this is the only way I can see to improving any imbalance there may be. I do not know of any devices etc out in the market for a quick fix

-------------------------
Stevie H
 11 October 2009 07:27 PM
User is offline View Users Profile Print this message



fredman

Posts: 221
Joined: 26 July 2007

totaly agree on this, to find out if you have a real imbalance you need to record over a day / week to get an overall average.
you would also need to look at the standing 3 phase base load and then the single phase loads.

As an imbalance it is not bad have seen far worse.
 13 October 2009 06:32 AM
User is offline View Users Profile Print this message



ablelectrical

Posts: 24
Joined: 04 August 2009

Thank you for all the input. Looks like i'm stuck with ye good ol data logger and many hours with my faithfull clamp meter!! As far as imbalances go, yes i've seen worse too and that may just have been a particularly busy time of day and probably does not reflect the real consumption (which is where the data logger would come in). But let's say the readings are true - and based on the knowledge that a three phase meter reads at the highest current? - even being able to balance the loads by 10% still offers a substantial saving for the heavy consumers, no? Or maybe i've missed the boat....
 13 October 2009 07:19 AM
User is offline View Users Profile Print this message


Avatar for sfchew.
sfchew

Posts: 589
Joined: 10 December 2002

The unbalance in loading is anticipated in design. Unless it impacts on the supply system parameters it is usually left alone.

There is no significant advantage in keeping the phases perfectly equal. Neither is there any gain in energy saving.


Regards
Chris Chew