Topic Title: Primary Injection & Secondary Injection Test
Topic Summary:
Created On: 12 October 2006 05:00 AM
Status: Read Only
Linear : Threading : Single : Branch
1 2 Next Last unread
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 12 October 2006 05:00 AM
User is offline View Users Profile Print this message



geeli

Posts: 61
Joined: 21 April 2005

having post the same topic on the Wiring & Regulation Thread and received no reply hence decide to put it at this Thread (Power Sector)

1) how do one conduct a PI and SI test?

2) is the any good website showing pictures of how such a test is to be conducted and the cabling that is to be connected to the terminal.

3) would appreciate if there is a step by step procedure on such a test.

thanks.
 12 October 2006 10:04 AM
User is offline View Users Profile Print this message


Avatar for duncan_gould.
duncan_gould

Posts: 114
Joined: 19 April 2002

Geeli,

Primary and secondary current injection tests are normally conducted to check the operation of breaker and their protective relays/devices.

The protective devices installed vary from circuit to circuit depending on the protection needs and philosphy but typical relays/devices include overload, over current, reverse power, earth fault, differential protection, etc., etc.

Primary injection testing normally involves injecting the actual current required to operate a protective device power through the circuit breaker.

Primary injection testing normally requires specialist injection sets/test rigs and measurement equipment (particularly for high power and MV and above) and can be extremely arduous where the circuit breaker interrupts large currents, shortening its life or requiring repair after. In many cases, primary injection testing is only conducted by specialists and in some cases primary injection testing may not be required through life.
Testing and research of this form is certainly carried out by circuit breaker manufacturers. Primary injection testing may be the only means of testing some LV circuits.

Secondary injection testing is normally different to primary injection testing because it is normally conducted when the circuit breaker is closed but is not carrying any current throught its main poles.

Secondary injection testing normally involves disconnection of the protective device from it's normal VT/CT and connection to a specialist test set that can inject and measure/record the required operating signal directly into the protective device relay to cause it to operate the circuit breaker.

The advantage of secondary injection testing is that the circuit breaker does not have interrupt large current and only low voltage signals are injected to operate the device.

A perceived disadvantage of secondary injection testing is that the actual operation of the 'whole' system is not tested but this may be compensated by the fact that the circuit breaker has operated without having to interrupt a large current and the circuit breaker type has tested and rated by its manufacturer.

However, specialist equipment and knowledge is still required, including significant knowledge of the actual protection scheme and philosophy. Furthermore, disconnecting of VT/CT can also lead to potential danger. For this reason, secondary injection testing is also often conducted by specialists.

In other words, it is not something that is jumped into without significant experience and knowledge.

The book Protection of Industrial Power Systems by T. Davies may be of interest, or try an internet search for the GE Art & Science of Protective Relaying.

I hope that's helpful.

Duncan

-------------------------
Duncan

Edited: 12 October 2006 at 10:07 AM by duncan_gould
 12 October 2006 10:21 AM
User is offline View Users Profile Print this message



cheewah

Posts: 11
Joined: 17 May 2006

a. PI & SI are normally referring to the CT's Primary & Secondary Injection current depending on the purposes i.e. setting of protection, instrumentation, etc and depending on CT's of ?/5A or ?/1A.
b. Due to the danger and risk involved, we normally apply SI: However, we still apply PI if neccessary.
c. I am a Commissioning & Servicing Engineer up to 33 KV. You can write to me directly by my e-mail to cmeelectrical@yahoo.com & my W/S is Link removed/cmeelectrical
d. Good luck!

Cheewah
 12 October 2006 10:32 AM
User is offline View Users Profile Print this message



cheewah

Posts: 11
Joined: 17 May 2006

Mr Duncan,
a. SI rather tha PI is normally employed as you have already explained.
b. For recalibration & maintenace, we normally encourge to carry out the tests on CT's including the ratio test.
Best rdgs
cheewah
 12 October 2006 10:48 AM
User is offline View Users Profile Print this message


Avatar for duncan_gould.
duncan_gould

Posts: 114
Joined: 19 April 2002

Cheewah,

a. agreed.

b. agreed, this would be the norm.

Given your position, would you agree it is important to highlight the need for competence and experience in praticing in this area in addition to helpful tools such as step-by-step procedures for every installation?

BR,

Duncan

-------------------------
Duncan

Edited: 12 October 2006 at 11:21 AM by duncan_gould
 12 October 2006 12:29 PM
User is offline View Users Profile Print this message



geeli

Posts: 61
Joined: 21 April 2005

To Mr Duncan
thank you for the explanation and the great website you have given. it is indeed a good site. i am still in the process of downloading the PDF for my leisure read.

To Mr Cheewah
thanks for your contribution too. however at the present moment i am unable to engage your service :-)

My understanding of the injection tests is as follow

Primary Injection Test
1) to ensure wiring connection of protection system is correct
2)to check CT ratios and polarities
3) to check Overcurrent relays and Earth Fault relays (both DTL type) are set to correct setting
4) to check Direct Acting Tripping element of the main MCCB.

Secondary Injection Test
1)If the protection relays (overcurrent and/or earth fault relays) are IDMTL type then Secondary Injection Test is required.

As such having read the replies. i am a bit puzzled why PI is less used and SI is more commonly being used.

Are not all Main Switchboard protection relays need to be tested and sealed before energisation?

I am referring to all Low Voltage 3 phase 400V switchboards with current ranging from 200A to 1000A.
 12 October 2006 12:51 PM
User is offline View Users Profile Print this message


Avatar for duncan_gould.
duncan_gould

Posts: 114
Joined: 19 April 2002

Geeli

As such having read the replies. i am a bit puzzled why PI is less used and SI is more commonly being used.

Primary injection testing normally requires specialist injection sets/test rigs and measurement equipment (particularly for high power and MV and above) and can be extremely arduous where the circuit breaker interrupts large currents, shortening its life or requiring repair after.


The advantage of secondary injection testing is that the circuit breaker does not have interrupt large current and only low voltage signals are injected to operate the device.




it is important to highlight the need for competence and experience in praticing in this area in addition to helpful tools such as step-by-step procedures for every installation




I hope that helps,

Duncan

-------------------------
Duncan

Edited: 12 October 2006 at 12:53 PM by duncan_gould
 14 October 2006 02:37 AM
User is offline View Users Profile Print this message



cheewah

Posts: 11
Joined: 17 May 2006

Mr Duncan,
a. Fully agreed with you.
b. Tester must be qualified and examined particularly for his practical skill before they are allowed to go for site testing. Proper authorisation from the the right 'authority' is highly recommended!
c. Furthermore, he must be well disciplined and sincerely in carry out these trust-worthy tasks as it involves the 'real time protection' of human lives, equipments and the buildings as well.
d. I am a Malaysian and work in Malaysia. Therefore I must follow Malaysia's guidelines and standards.
e. Mr Duncan, thanks for your contribution, guidance and idea-sharing.
Best regards
Cheewah
 18 October 2006 11:54 AM
User is offline View Users Profile Print this message



geeli

Posts: 61
Joined: 21 April 2005

Primary Injection Test (PI Test)
1) to ensure wiring connection of protection system is correct
2)to check CT ratios and polarities
3) to check Overcurrent relays and Earth Fault relays (both DTL type) are set to correct setting
4) to check Direct Acting Tripping element of the main MCCB.

Secondary Injection Test (SI Test)
1)If the protection relays (overcurrent and/or earth fault relays) are IDMTL type then Secondary Injection Test is required.

I would like to confirm and reassure myself that my understanding of the above two tests
serve different purposes and its purposes are as stated above.

Am i correct?

Would appreciate replies.
 27 October 2006 01:25 AM
User is offline View Users Profile Print this message



deleted_Colhind

Posts: 6
Joined: 06 September 2006

G'day,
Primary injection (sometimes referred to as a trip test) is generally carried out as a test to determine the integrity of the whole secondary protection circuit including CTs, CT leads and control cubicle wiring. In other words it proves that the CB trips in response to an overcurrent. The test is performed after secondary injection tests and CT ratio tests and when all the secondary test links are closed and ready for service. Hence it is often the last test perfomed in the commissioning process.

The PI test is usually performed by injecting a current at low volatage (say 5 -10 V) from a purpose built transformer with high current capable secondary winding. The current is passed through the breaker or busbar section as appropriate. The magnitude of current injected is generally not considered important so long as it is above the minimum operating current determined by the protection relay settings. Sometimes the current and time to trip is measured but owing to the inability to provide currents as large as the prospective HV fault currents no attempt is made to perform full Time-Current Characteristic tests of the protection scheme.

Secondary injection tests are performed by injecting currents into the relay terminals to determine that the relay is operating correctly and in accordance with its settings. Such tests are usually carried out in the control room at test links provided for the pupose. These tests include injecting currents of various magnitudes from MinOp all the way up to 10 or 20 times MinOP and measuring the relay operating time if your test equipment is up to the task. Anything less than 10 times MinOp and you will need to carefully the risk of the relay being off characteristic at the higher currents and what affect that might have on co-ordination with other schemes.

CT ratio tests are performed to determine that the relationship between primary current and secondary current seen by the relay is correct.

CT saturation tests are also performed as proof that the CT is up to the job of providing accurate output at the prospective fault levels.

Having performed these tests you have done all that is reasonable to prove the correct operation of the protection scheme.
 30 October 2006 11:52 AM
User is offline View Users Profile Print this message



geeli

Posts: 61
Joined: 21 April 2005

thanks Colhind for your reply.

however i am cofused at the moment between your elaboration on the primary injection (sometimes referred as trip test) and the PI test.

aren't PI test is termed as primary injection test?

i am fully aware that there are lots of electrical professionals in the forum however am upset that the replies to this thread is wanting.

it might be that there are people that can perform those tests but are not sure where to term those tests.. just my thought.

i am sharing with Colhind on this as you are the last person to share your view after a number of days lapse...
 02 November 2006 09:58 PM
User is offline View Users Profile Print this message



deleted_1_rbcatlow

Posts: 15
Joined: 15 September 2001

Drop me a line at rbcatlow@aol.com if you need more information

My team do primary and secondary injection tests every week from 11kV to 132kV on a weekly basis

Richard

-------------------------
rbcatlow
 23 November 2011 07:45 AM
User is offline View Users Profile Print this message



NickCarter23

Posts: 1
Joined: 16 March 2009

Does anyone know where I can buy a decent secondary injection tester?

Looking to secondary injection test a MiCOM Electronic Protection Relay?

Cheers

Nick
 23 November 2011 08:35 AM
User is offline View Users Profile Print this message



ArthurHall

Posts: 737
Joined: 25 July 2008

If you are just doing a few relays I would hire a test set. If you are in the UK there are a few companies that hire them. You could try Cuthbertson & Laird as one example.
A basic test set will cost at least £1500 going up to about £30000.
Dont be tempted to make do with a transformer and variac as distorted waveforms could give you false results.
 23 November 2011 12:15 PM
User is offline View Users Profile Print this message



AdrianWint

Posts: 269
Joined: 25 May 2006

Slightly OT..... AREVA/ALSTOM documentation seems to suggest that SI testing is no longer considered necessary with digital protection relays.

What is the general feeling on this?

Adrian
 23 November 2011 03:42 PM
User is offline View Users Profile Print this message



ArthurHall

Posts: 737
Joined: 25 July 2008

The relays may be OK but what about the wiring and trip relays?

IMHO Primarys are done once on commissioning after that it is only required to carry out an insulation resistance check at 1000 or 500 Volts.

Secondary injection tests are carried out at regular intervals and should include a trip through to the breaker.

Communications channels usually need testing more frequently that secondary injection tests.

Trip tests should be carried out at least annually
 23 November 2011 07:01 PM
User is offline View Users Profile Print this message



Peddler

Posts: 36
Joined: 28 May 2008

I'll throw my tuppence in,

got to aggree with Arthur usually after commissioning, primary Injection is not periodically required. If the CT was commissioned and is wasn't upside down at commissioning and start up stage then its not likely to be after it. Same goes with the ratio, and how many people here have had many problems with saturation after being commissioned by a specialist?. In my experience it's the actual relay that causes the most problems, perhaps the response curves need adjusted if inrush is a problem etc etc. This is normal "bath tub curve" theory once your handing over a project or signing a handover certificate anyway.
I remember years ago we carried around cumbersome and heavy injection sets, Injected lots of overload relays for motor protection etc and I must confess I sure we caused some of them to have smoke belching out of them . probably weakened perfectly good thermal overload relays.
My advice is not to do this type of testing unless you know exactly what your doing, go on a protection course , there's one up at ASET in Aberdeen. Good Course.
Also the injection testing is the easy bit , its the designing of the protection system that's the real skill. You got to admire those protection Engineers , its art work.

P

-------------------------
You can Learn from an Apprentice
 23 November 2011 08:20 PM
User is offline View Users Profile Print this message


Avatar for JonathanHill.
JonathanHill

Posts: 225
Joined: 09 September 2002

I'm highly suspicious of claims that SI of electronic/ microprocessor/ numerical relays is not necessary. Recent, bad, experience of a project where limited relay testing was carried out convinces me that this is required.

The complete trip circuit needs verification from CTs to trip action in any event so I'm with Arthur (and others) and would insist on Primary & Secondary Injection on 1st commissioning (including trip tests), followed by periodic reruns of SI at intervals <5yrs. During these periodic maintenance, the battery condition should also be reviewed. Personally, for VRLA (sealed lead-acid) type batteries, which should be specified as 10-yr design life as per Part 4 of BS ????, I'm in favour of replacing these at 5 or 6-yearly intervals.

-------------------------
Jonno
 23 November 2011 10:14 PM
User is offline View Users Profile Print this message



alancapon

Posts: 5831
Joined: 27 December 2005

I would agree with the comments above. Primary Injection on initial commissioning and if the CTs are replaced, otherwise Secondary Injection into the relay. Either way, I like to see the circuit breaker trip at least once as a result of the injection. There is a bit of a controversial view held by an employee of a company that makes test sets, but even he suggests that it is important to Secondary Inject to prove the relays are reading the correct currents / voltages, and also prove all the output contacts are still working.

I believe that the important thing with a modern electronic relay on commissioning, is not only to prove that it will do all the things you want it to do, but also prove that it won't do all the things you think you have turned off in the software!

Regards,

Alan.
 31 August 2012 07:10 AM
User is offline View Users Profile Print this message



squelch

Posts: 2
Joined: 31 August 2012

Good read.. BM