Hi just after a little advise if anyone could help please. Iv got to change a switched fuse in a form 4 panel from a 32A to a 64A and upgrade the tails to the bus bars, the existing bus bars would not need any modification. The customer wants me to certify the modification. I'm at a bit of a loss where to start the MCC is about 15years old and i have no information other that what i can ascertain from a visual inspection. Any help would be much appreciated.

Thanks
Nathan
 10 January 2014 12:23 PM
User is offline View Users Profile Print this message



oneye

Posts: 187
Joined: 25 February 2008

Hi Nathan,

You have not mentioned existing drawings or any other paperwork.

IMO if there is no original Test or Installation Certificates, then I would take the view that, whilst the existng busbars would be more than adequate, you may change the short circuit characteristics of the whole board.
This would then need a full technical appraisal for re-Certification.

Otherwise you would be amending the original Certification.