Hi All

IEEE 519 Table 10-3 states max harmonic levels (% of IL) fro Isc/IL ratio up to 50 as:
<11 harmonics - 7%
11 to 17 - 3.5%
17 to 23 - 2.5%
23 to 35 - 1%
35 - 0.5 %
TDD 8%

We are replacing a UPS, 110Vdc system.

Anyone any experience on achieving the above specification? The manufacturers are suggesting a 12 pulse rectifier with incoming filter. However some correspondence would suggest this may be difficult to a cost effective achieve.

Anyone any experience to share here?