Topic Title: Power requirements
Created On: 02 July 2012 10:16 AM
Sparky64
I have been asked to calculate the power requirements for a new electrical installation in order to specify cable and MCCB sizes. This is something i have never done before and would like to know how i go about it.
I was going to add up all the Motor & transformer KW/KVA ratings and then calculate my current from this, is this correct?
Do i have to calculate the power requirements for every single device, every contactor and relay?
Any help would be greatly appreciated.
 05 July 2012 11:23 AM
Avatar for neilparsons.
neilparsons
Just adding all the loads up on all but the smallest installation may give a pessimistically high maximum demand.
You need to look at diversity (how many of the loads will be on at the same time) and utilisation factors (will a load, say a motor be used to its maximum).
By applying diversity and utilisation factors you should come up with a realistic figure, you then need to add a bit (could be 25%) for future expansion.
You normally need to have a good understanding of how the installation will be used. You can also use power monitoring if you have a similar existing installation.
 16 October 2012 06:37 PM
Avatar for MAXMIRA.
MAXMIRA
Sparky, I'd recommend first listing all of the loads then looking at them on an individual basis before applying an overall diversification.
 23 October 2012 12:41 PM
alexmoroz1987
I agree with Maxmira. you have to look on an individual basis. Hope you will be able to sort it out.
 10 March 2013 05:08 PM
deepakjnu10