Hi All,
I have a problem which may have a simple solution but I just wanted to make sure that I was going the right way. I have a load which draws 40A of current at 48V. I am seting up battery banks which can provide power for 4 hours minimum. With all other factors, required battery capacity comes upto 388 Ahrs. I have 4 batteries (48V, 150A) in series to form a bank/string. So I will require minimum of 3 strings of batteries (450Ahrs) in pararllel to meet the requirement. Now the question is.... For N+1 setup, can I just have 4 strings of batteries in parallel to full fill the required redundancy set up or will I need 6 strings in parallel (i.e. 3strings+3strings). I am thinking its 6 strings but just wanted to make sure. Hope someone could help me with this confusion. Thank you in Advance. Amar. Battery Set up |---------------0 Load 0----------------------| | | |---B1-----------B2--------B3--------B4----| | | |---B1-----------B2--------B3--------B4----| | | |---B1-----------B2--------B3--------B4----| ........... ...... ... Edited: 04 November 2010 at 01:16 PM by amarlama |
|
|
|
|
|
|
|
|
If you are wanting redundancy to manage single fault condition, then you need only one more string of cells than required to meet normal use current requirements - the redundancy is to cover the case of any one cell (string of cells) going open-circuit.
So with 3 strings required by design (N = 3), you would need 4 (N+1) to comply with the redundancy requirement. |
|
|
|
|
|
|
|
|
If you are wanting redundancy to manage single fault condition, then you need only one more string of cells than required to meet normal use current requirements - the redundancy is to cover the case of any one cell (string of cells) going open-circuit. So with 3 strings required by design (N = 3), you would need 4 (N+1) to comply with the redundancy requirement. My initial thoughts were similar, its just I got the second thought of assuming N being 3 strings and for back up similar second set up hence requiring 6 strings. But its making more sense to have 4 strings for N+1.. then 6 strings or else it would have been 2N setup.. Thanks for the help Paul. |
|
|
|
|
|
IET
» Electronic engineering
»
N+1 Redundant setup help
|
Topic Tools |
FuseTalk Standard Edition v3.2 - © 1999-2013 FuseTalk Inc. All rights reserved.