Topic Title: Can anyone share a 3-wire instrument loop sheet?
Topic Summary: 3 wire gas sensor
Created On: 08 August 2012 09:03 AM
gadge
I've never worked with 3 wire instruments before so this is a new one to me.
I'm installing 3-wire gas sensor's in a haz area that will go direct into our siemens S7 PLC (iSP haz area I/O).
Apparently the loop power is not enough so i have to supply the sensor with external power and use a 4-wire AI card abd set the sensor as source and not sink powered.
Has anyone got a loop of how this should be wired?
 08 August 2012 02:26 PM
JohnLindop
The ones i have used have:
3 wires or connections
+v (Brown wire) positive from power supply.
sig (Black wire) signal wired into input of PLC I/O.
0v (Blue wire) 0v from power supply.
Not sure about the wiring of a IS module from Siemens but a would guess that the 4 th terminal should be tied to either 0v or signal.
Best of luck.
John
 15 August 2012 04:01 AM
alamatec
2 of the wires provide power to the instrument +24V DC & 0V DC. The third wire provides the current drive to the card 4-20mA. So you are correct that the instrument is the source. Make sure that both the instrument and the I/O card use the same power supply.
 28 August 2012 09:22 AM
chartassuk
Hello gadge,
Additional criteria to be satisfied with the proposed loop is that Intrinsic Safety (or the agreed concept of explosion protection) is achieved.
 14 October 2012 08:28 AM
gadge
Thanks for replies. Didnt get notification for some reason, anyway..
I set the gas sensor up on the bench, with a 24vdc supply going to the sensor across + and 0V, and for the signal out i doubled up on the 0V and 4-20mA +. I was getting the correct mA reading on the multimeter.
Good point about using the same PSU, i was going to use a seperate one, only because i dont think there are any spare ways off the PSU supplying the ET200 iSP PLC.
 17 October 2012 02:51 PM
Avatar for MAXMIRA.
MAXMIRA
Just a note to say beware that you do not infringe the I.S. integrity of the device. I would carefully read the atex cert of the gas sensor and also explore the possibility of using a galvanic device driver.
 17 December 2012 07:10 AM
RockWood
3-wire connections means It's +24 , 0 Vdc & signal (+)