IET
Decrease font size
Increase font size
Topic Title: Loop impedance measurement through an inverter
Topic Summary:
Created On: 30 March 2012 02:15 PM
Status: Read Only
Linear : Threading : Single : Branch
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 30 March 2012 02:15 PM
User is offline View Users Profile Print this message



dougflorence

Posts: 74
Joined: 25 July 2008

I am looking at doing earth loop impedance measurements on a machine to determine if the fusing on inverter supplies is suitable for EN60204 compliance. E.g. using an installation tester such as Metrel MI 3000.

No problem with conventional motors, but what about servo motors and motors powered by inverters?

Any risk of damage to the inverter? I guess not because all the tester does is create a 2 cycle earth fault and measure the current during the fault. Most modern inverters can take that sort of thing in their stride.

Will it get meaningful results anyway?
 06 May 2012 01:53 AM
User is offline View Users Profile Print this message



johnboy6083

Posts: 50
Joined: 25 July 2008

You won't get results, as the drive will see it as a fault. Also the cables from the VSD are protected by that. If you need an impedance value to satisfy the paperwork, then use Zs= Ze +(R1+ R2).
The drive instructions often have max cable lengths and cable sizes in the manuals anyway.
 12 June 2012 12:30 PM
User is offline View Users Profile Print this message



Jonni1987

Posts: 9
Joined: 01 July 2011

If completing a live test, which I presume you are, could you not complete the test across the inverter?
 18 June 2012 04:01 PM
User is offline View Users Profile Print this message



phayton

Posts: 9
Joined: 03 January 2006

The input of the variable speed drive will have capacitors connected line to chassis which will confuse the 4 cycle pulse from the tester.
A more reliable test would be achieved with the inverter drive disconnected.
Statistics

See Also:



FuseTalk Standard Edition v3.2 - © 1999-2016 FuseTalk Inc. All rights reserved.


..