 02 December 2011 10:58 AM
User is offline View Users Profile Print this message



cdaly2001

Posts: 5
Joined: 14 August 2010

What will happen if you try and use a UPS that is rated as 1.1 A max out current to supply a system that demands 2.5 amps? Will the UPS just discharge faster or will the system fail?
 02 December 2011 11:18 AM
User is offline View Users Profile Print this message



ArthurHall

Posts: 720
Joined: 25 July 2008

both.
If it tries to supply the load the batteries will discharge quicker but the output electronics will be overloaded and will probably fail. If the unit has output protection it will just sit down and give no output.
 02 December 2011 11:20 AM
User is offline View Users Profile Print this message



cdaly2001

Posts: 5
Joined: 14 August 2010

What about using two UPS in parallel?
 02 December 2011 11:20 AM
User is offline View Users Profile Print this message



cdaly2001

Posts: 5
Joined: 14 August 2010

What about using two UPS in parallel?
 02 December 2011 11:52 AM
User is offline View Users Profile Print this message


Avatar for gkenyon.
gkenyon

Posts: 4392
Joined: 06 May 2002

Originally posted by: cdaly2001

What about using two UPS in parallel?
Not possible for a number of reasons, unless the manufacturer has specifically stated it can be done with their range of products.

What about a bigger UPS?

-------------------------
Eur Ing Graham Kenyon CEng MIET
 02 December 2011 11:58 AM
User is offline View Users Profile Print this message



cdaly2001

Posts: 5
Joined: 14 August 2010

That would be the ideal solution but the customer needs a non battery type UPS and the only one in our range is 1.1A. Just out of interest what are the reasons?
I knew it was a long shot :-)
 04 December 2011 02:23 PM
User is offline View Users Profile Print this message



oneye

Posts: 121
Joined: 25 February 2008

"...customer needs a non battery type UPS.."
What kind of energy source would your customer be looking for ?

You have not stated voltage.
If it's 230vAC then at 1.1 amp is not exactly a large UPS.
 04 December 2011 05:41 PM
User is offline View Users Profile Print this message


Avatar for gkenyon.
gkenyon

Posts: 4392
Joined: 06 May 2002

Originally posted by: cdaly2001

That would be the ideal solution but the customer needs a non battery type UPS and the only one in our range is 1.1A. Just out of interest what are the reasons?

I knew it was a long shot :-)
To link the UPS together, you'd need to statisfy a number of criteria:

1. Output voltages can be "phase-locked", so they are both rising and falling precisely together.

2. Need to make sure one can't back-feed the other in any way.

3. May need to make sure that the frequencies of the switching converters are precisely the same and are phase-locked too, otherwise may mean that the voltage/current output generates a lot of noise: EMC issues.

But surely if this is in your range, your tech guys know the answer?

-------------------------
Eur Ing Graham Kenyon CEng MIET
 05 December 2011 07:53 PM
User is offline View Users Profile Print this message



mike.mcclory

Posts: 30
Joined: 26 April 2006

If you try to overload a UPS by that much the chances are that the output protection will trip either from the over-current or output voltage droop. You could probably find some way to parallel them, buy why add that level of complication?