What will happen if you try and use a UPS that is rated as 1.1 A max out current to supply a system that demands 2.5 amps? Will the UPS just discharge faster or will the system fail?
|
|
|
|
|
|
|
|
|
both.
If it tries to supply the load the batteries will discharge quicker but the output electronics will be overloaded and will probably fail. If the unit has output protection it will just sit down and give no output. |
|
|
|
|
|
|
|
|
What about using two UPS in parallel?
|
|
|
|
|
|
|
|
|
What about using two UPS in parallel?
|
|
|
|
|
|
|
|
|
What about using two UPS in parallel? What about a bigger UPS? ------------------------- Eur Ing Graham Kenyon CEng MIET |
|
|
|
|
|
|
|
|
That would be the ideal solution but the customer needs a non battery type UPS and the only one in our range is 1.1A. Just out of interest what are the reasons?
I knew it was a long shot :-) |
|
|
|
|
|
|
|
|
"...customer needs a non battery type UPS.."
What kind of energy source would your customer be looking for ? You have not stated voltage. If it's 230vAC then at 1.1 amp is not exactly a large UPS. |
|
|
|
|
|
|
|
|
That would be the ideal solution but the customer needs a non battery type UPS and the only one in our range is 1.1A. Just out of interest what are the reasons? I knew it was a long shot :-) 1. Output voltages can be "phase-locked", so they are both rising and falling precisely together. 2. Need to make sure one can't back-feed the other in any way. 3. May need to make sure that the frequencies of the switching converters are precisely the same and are phase-locked too, otherwise may mean that the voltage/current output generates a lot of noise: EMC issues. But surely if this is in your range, your tech guys know the answer? ------------------------- Eur Ing Graham Kenyon CEng MIET |
|
|
|
|
|
|
|
|
If you try to overload a UPS by that much the chances are that the output protection will trip either from the over-current or output voltage droop. You could probably find some way to parallel them, buy why add that level of complication?
|
|
|
|
|
|