Topic Title: Analogue input to PLC bounds checking regulations
Topic Summary: Analogue PLC input standards
Created On: 05 January 2011 10:14 AM
mccted
Hi,
I'm trying to justify our handling of safety analogue inputs in to a PLC. We check for above and below range (outside fo 4 -20mA), but is anyone aware of a standard where the exact requirements for this are defined? I beleive there is something in the German NAMUR specifications.
Thanks,
Daniel
 06 January 2011 02:54 PM
chartassuk
Hello mccted,
Some questions:
If the signals perform a safety function, should they be handled by a PLC?
Have the Safety Requirements and Safety Instrumented Function been defined?
if they have, is there a resultant SIL?
Is the PLC rated to this SIL?
Have you considered appropriately SIL rated dedicated trip-amps?
I'm not being obtuse but interested in what it is you're controlling.
 07 January 2011 04:28 PM
mccted
Yes it is part of a SIF to a SIL 3 rated PLC (German manufacturer starting with S!), all the documentation is done pretty much with IEC 61511 in mind.
I was just trying to check what I had put about the bounds checking, as I had some comments from auditors about NAMUR requirements for bounds checking. I've got the usual things from the IO channel driver library block defined to cover checking and all I can find out on NAMUR is that it needs to check the signal is within 3.6mA to 21mA. I was wondering if there was any guidance or something in an EN / BSi standard I could look at as I don't have access to any NAMUR information or much knowledge of it. Really so I can add anything else or feel happy I have covered everything I need to.
The inputs are only from simple transmitter, no use of HART or such like.
 07 January 2011 05:19 PM
chartassuk
Hi again mccted,
The NAMUR recommendation is:
NE 043 Standardization of the Signal Level for the Failure Information of Digital Transmitters - (57 KB) - 104422680003.02.2003
02/03/2003 AK 3.1 - Signal Processing
available free from the NAMUR portal http://nena.namur.de/index.php?id=6
hope this helps
 12 January 2011 04:33 PM
mccted
Thanks for your help chartassuk , much appreciated.