Topic Title: 24Vdc circuit protection Topic Summary: Control panels Created On: 28 January 2010 10:30 PM Status: Post and Reply |
Over the years, I've seen several different methods of circuit protection for 24Vdc circuits in control panels. Examples being:
Double pole MCB on PSU 24Vdc output protecting all control circuits Each field component protected by own fuse Groups of field components protected by single fuse Each PLC I/O card protected by own fuse No 24Vdc circuit protection at all I was interested to see how other people involved in panel manufacture & maintenence approach this. |
I would expect to see overcurrent protection at source. Single pole if one line is earthed. Double pole if no earth or centre tap earthed. Check that the device is suitable for DC, at higher voltages you often have to connect devices in series as the contact gap is too small to break a DC arc.
I have alaways used MCB protection for protection of the PSU Outputs, usually double pole on the +24VDC line. Many of my clients have their own set of drawing standards which will include all, or some of the methods listed by Scrumpy.
If on the rare ocasion I have a freehand at specifiying! then I would go for the following: Double pole MCB on the main +24VDC line supplying suitably rated single pole MCB's for the following: "General Control" - All Control Lamps and Sensors etc "PLC Supply" - Power for PLC Supply only "PLC Inputs"- All PLC Input supplies (one or more MCB dependant on size of PLC and your choice of isolation) "PLC Outputs" All PLC Output supplies (one or more MCB dependant on size of PLC and your choice of isolation) "HMI / Instrumentation" - as stated. "Safety" - all Safety specific equipment PILZ realys / light guard supplies etc. And, cost as always plays a role, some clients opt for fuses (usually the utility companis I work for!) as this is the cheaper option! Hope this helps Ian. |
Have seen self resetting multifuse/polyfuses (e.g. Bourns) too for lower current apps (<5A). (On boards within CP that is.)
Regards E. ------------------------- ~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~~ The meaning of life is a blank sheet; write on it wisely. ~ M.Cutler. |
» Control and automation