I understand that red is used to identify ac control circuits within a control panel. I'm looking to discriminate between 110 and 24Vac. Excluding yellow and green, is there a colour commonly used for 24Vac
|
|
|
|
|
|
|
|
|
Generally, I don't think you can go far wrong if you follow EN60204-1 for control wiring. This is the "Machinery" industry standard for electrical safety, and does cover "controls".
------------------------- Eur Ing Graham Kenyon CEng MIET |
|
|
|
|
|
|
|
|
Many thanks
|
|
|
|
|
|
|
|
|
The quoted Spec is a little vague, generally the end user specification dictates wire colours to be consistent with other panels on their site.
24Vdc tends to be red/black, 24Vac could be light blue / dark blue but that can easily confuse 110Vac brown/blue. Some have 24Vac orange/orange whereas other clients have orange/orange to be voltfree non isolated external supply @ any voltage. You need to nail down what colours are acceptable before you start. |
|
|
|
|
|
|
|
|
The quoted Spec is a little vague, generally the end user specification dictates wire colours to be consistent with other panels on their site. 24Vdc tends to be red/black, 24Vac could be light blue / dark blue but that can easily confuse 110Vac brown/blue. Some have 24Vac orange/orange whereas other clients have orange/orange to be voltfree non isolated external supply @ any voltage. You need to nail down what colours are acceptable before you start. All panels I have worked on previously had the ac/dc colours opposite to the quote above. Whilst I agree the spec is vague & BS EN 60204-1:2006 is the standard to work too. See paragraph 13.2.4. Red = ac control circuits at any voltage. Black = ac & dc POWER circuits at any voltage. Blue = dc control circuits at any voltage. Orange = excepted circuits according to para 5.3.5. White tends to be functional earths, taken from BS7671. There is a few colours that you can use, but as per previous post, get customer specs, or at least written agreement. You can't use, yellow, green or green/yellow if it may be confused! I have only seen orange "live with main isolator off" that is fed from another source. Not seen brown in a control panel except incoming (new colours) and in special multicore cables, signal wiring etc. There are other relevant standards as well depending on the equipment. HTH Paul |
|
|
|
|
|
|
|
|
A couple of years ago I put together a spread sheet on wire colours. Copying / pasting doesn't work to well in the forum but this should identify what was current 2 years ago (still think it is but not checked)
Hope it helps Regards Howard Wheeler Phase L1 BS 7671:2008 - Brown BS EN 60446:2000 Brown & Black preferred BS EN 60204-1:2006 no comment Phase L2 BS 7671:2008 - Black BS EN 60446:2000 Brown & Black preferred BS EN 60204-1:2006 no comment Phase L3 BS 7671:2008 - Grey BS EN 60446:2000 Brown & Black preferred BS EN 60204-1:2006 no comment Neutral BS 7671:2008 - Blue BS EN 60446:2000 Blue BS EN 60204-1:2006 Light blue Single Phase live, L1 BS 7671:2008 - Brown BS EN 60446:2000 & BS EN 60204-1:2006 no specific comment Single Phase neutral, N1 BS 7671:2008 - Blue BS EN 60446:2000 & BS EN 60204-1:2006 no specific comment Protective conductor BS 7671:2008 - Green/Yellow BS EN 60446:2000 Geen / Yellow BS EN 60204-1:2006 Green / Yellow PEN BS 7671 Green/Yellow with blue markings at terminations or Blue with green/yellow markings at terminations BS EN 60446:2000 & BS EN 60204-1:2006 no comment Colours not to be used BS 7671 Green BS EN 60446:2000 & BS EN 60204-1:2006 no comment Functional Earthing conductor (e.g signal earths?) BS 7671 Cream BS EN 60446:2000 & BS EN 60204-1:2006 no comment D.C. (floating) positive (POWER CCTS) BS 7671 Brown BS EN 60446:2000 & BS EN 60204-1:2006 no comment D.C. (floating) negative (POWER CCTS) BS 7671 Grey BS EN 60446:2000 & BS EN 60204-1:2006 no comment D.C. Positive (neg earth system) (POWER CCTS) BS 7671 Brown BS EN 60446:2000 & BS EN 60204-1:2006 no comment D.C. Negative (neg earth system) (POWER CCTS) BS 7671 Blue BS EN 60446:2000 & BS EN 60204-1:2006 no comment D.C. Positive (positive earth system) (POWER CCTS) BS 7671 Blue BS EN 60446:2000 & BS EN 60204-1:2006 no comment D.C. Negative (positive earth system) (POWER CCTS) BS 7671 Grey BS EN 60446:2000 & BS EN 60204-1:2006 no comment Control Circuit positive BS 7671 Brown, Black, Red, Orange, Yellow, Violet, Grey, White, Pink or Turquoise BS EN 60446:2000 & BS EN 60204-1:2006 no comment Control Circuit neutral or mid wire BS 7671 Blue BS EN 60446:2000 & BS EN 60204-1:2006 no comment Conductors other than protective or neutral BS EN 60204-1:2006 Brown, Black, Red, Orange, Yellow, Violet, Grey, White, Green, Blue, Pink, Turquoise BS 7671 & BS EN 60446 No comment A.C. & D.C. power circuits BS EN 60204-1:2006 Black BS 7671 & BS EN 60446 No comment A.C. control circuits BS EN 60204-1:2006 Red BS 7671 & BS EN 60446 No comment D.C. Control circuits BS EN 60204-1:2006 Blue BS 7671 & BS EN 60446 No comment Excepted ccts (not disconnected by supply isolating device). Eg external interlock circuits, lighting etc see p27 of EN60204-1 -orange BS 7671 & BS EN 60446 No comment |
|
|
|
|
|