Topic Title: rcd test button
Topic Summary: mech requirement
Created On: 19 March 2006 08:20 PM
daveses
just a quicky.
if testing a rcd and trips within required time with meter, but does not trip when test button is pushed on rcd is this a code 1 on pir form.
thanks.
 19 March 2006 08:23 PM
kaichung
Yes - it's time for a new RCD.
 21 March 2006 07:04 PM
daveses
can you explain why this is when the rcd operates fine under fault conditions. is it just because the consumer canot test it ?
 21 March 2006 07:09 PM
lbelectrics
I'd change this device as quarterly (press) tests are required for non-competent persons to ensure ongoing protection.
(yeah, like this will happen in reality!!!)
The fact that the device works electrically is comforting, but not good enough... grasp the nettle mate!
Lee
Astrostar
yes, this needs to be carried out quaterly as stated on the sticker that should be stuck on the consumer unit.
regards astro