Do all school kitchens have to have an emergency stop system for the power?
If so which standards or regulations is it in?
burn
 14 August 2014 12:37 PM
eclipse
It's usually for the gas! and associated with the BMS.
Thanks
Alan.
Now what was that reg no?
 14 August 2014 01:52 PM
OMS
Building Bulletin 100 suggests that school kitchens are "Places of special fire hazard" - whilst that relates to the use of the space, it's not uncommon for the EPO on the gas system to also act on the power systems.
BB 100 also suggest that fuel sources in "Places of special fire hazard" should be capable of being quickly isolated - so if you consider electricity as a fuel source, then the approach of the gas proving system with EPO which also acts on process power coupled with catering extract suppression as the best practice guidance