Topic Title: Cable Tray Stacking
Created On: 06 August 2014 08:15 AM
kumarm
Is there a BS code reference to the minimum allowable distance that a cable tray must be installed when placing the new tray system on top of another existing tray system? (i mean stacking)
 06 August 2014 08:50 AM
timothyarnold
Hi Kumarm
There is some guidance in Table 4C4 of BS7671 and suggests a minimum of 300mm however please note that it also states that the existing and new cable current carrying capacity will need to be de-rated as the ventilation is significantly reduced (depending on the number of cables, configuration etc).
To make life easier I would avoid stacking if you can!
Tim