Topic Title: SECTION 705 OF THE BGB
Topic Summary: A CONUNDRUM
Created On: 05 August 2014 11:26 PM
1 2 3 4 5 6 7 Next Last unread
John Peckham
As I am sure you all know 705.411.1 and 705.422.7 requires all circuits on a farm to be 300mA RCD protected for ADS and fire protection regardless of the earthing system (it's TNS).
On a farm I EICRed the electrical contractor is doing all the required remedial works to bring the farm up to current standards.
The farm is a dairy farm with some 1500 cows in sheds. The output from the cows is taken by scrapers and an in floor augur to a huge swimming pool size slurry tank. The slurry is pumped up in a large diameter pump to the top of a tower where rollers extract the solids and the liquid is pumped in to a further large tank. The very large pumps have VSD speed controllers. When running these VSDs trip the newly fitted 300mA RCD.
If this kit were to fail in the night because the RCD had tripped taking out all the power to the pumps would be a disaster.
I have told the contractor to take a separate non-RCD supply to the pumps for the moment whilst I have a think.
Given these pumps and tower are outside and have normal circuit protection and there is no hay , other than the wet contents of the tanks, I am thinking it would be sensible to omit the RCD protection for fire although this would be contrary to 705.
I would value your views especially from Stu L?
John Peckham
 05 August 2014 11:33 PM
I suspect if asked you know exactly what the earth leakage is on this equipment, so I'll ask what it is.
Andy
 05 August 2014 11:40 PM
John Peckham
I don't know the earth leakage on the particular piece of kit but it was high on the board supplying the whole installation due to a neutral to earth fault. I would imagine that the VSD is chucking out loads of harmonics and a high level of earth leakage. I know even small VSD will trip RCDs.
John Peckham
 05 August 2014 11:41 PM
Is it practical to measure how bad the earth leakage really is on each pump/control set?
If it is really anything like1/3 amp at 50Hz, that's a serious filter capacitance, I make it would have to be about 700j ohms, or 4uF L-E if it was single phase, and as I assume really 3 phase, then it must be more, but that 4uF is just the un-cancelled part !!
Could it be there is a wiring error, and there is a filtering star point that should be going to neutral, not to earth, or even an NE link fitted in the controllers ?
If its HF stuff causing the problem, then pre-filter down to neutral, not to earth, if required with the filter on spacers in an insulating enclosure to get the fast stuff off the lines and back up onto the L-L-L-N route rather than L-E.
some inverters have instructions for lifting the Y capacitors in this way for use on RCD protected supplies. The price is that stronger external filtering is then needed.
Is there something a bit like this anywhere
PWM reconstruction filters - see page 6 for waveforms
Or is there scope to comply in spirit and not in letter, and have more than one RCD (say one per pump) and get well below threshold that way.
If you have makers part nos for the controllers I may be able to get some info, before I have to vanish again.
edit fixed links - missed that it was https.
Also, if its nearly there then there is normally the option to change the PWM chopping frequency - if it is higher than need be, then lowering it reduces the number of pulses per second and therefore the general EMI background level, almost for free
Edited: 06 August 2014 at 01:37 AM by mapj1
 05 August 2014 11:45 PM
Zs
I'm thinking page two of the big green bumper fun book JP:
' Whilst the publisher and contributors believe that the information and guidance given in this work is correct, all parties must rely upon their own skill and judgement when making use of it...'
Then, given that, a sensible decision about the safety and protection of the beasts from electric shock and from other issues such as bacteria.
What do other establishments such as this do?
Zs
 06 August 2014 12:11 AM
I was going to keep it simple and ask the result of the ramp test on the RCD then compare it to the leakage to see the RCD had any chance of hanging on in there without all the fuzzy stuff in the system.
 06 August 2014 12:52 AM
I would expect the leakage to even out with a three phase supply. This leaves either Mike's suggestion of a wiring error, or the rcd is being affected by harmonics.
 06 August 2014 01:56 AM
Jaymack
I suspect that this tripping is caused on starting surges. If the VSD's are correct including the settings, a time delayed RCD would probably avoid this.
 06 August 2014 07:57 AM
Zs
Something you do have the technology for JP, is to log the earth leakage. Might tell you when things are happening and help to tie them down.
I'll not give all the secrets away on here but give me a ring if you want to hear how I set up on a TPN to achieve this.
Zs
 06 August 2014 10:05 AM
Parsley
 06 August 2014 10:22 AM
davezawadi
I have come across this too John, in many ways RCDs are not really very good. As said above the supply harmonics do not cancel in the leakage transformer, so larger loads instantly cause tripping. If this is the problem then a time delay will not work, but might be worth a try. VSDs do not normally have much 50Hz leakage, but may have quite a lot of other stuff, you could try an FFT of the supply currents on you analyser, more than a few percent of the 50Hz figure will cause tripping.
This section of the BGB needs revision, it seems to have been written by people who do not realise that farms can have very large electrical loads and 300mA is not necessarily suitable for modern equipment. If there were no VSD and a 50kW motor you would not be able to use an RCD anyway. As there is no fire risk, I would go with normal protection here, the RCD is both unworkable and unnecessary so the basic premiss in the BGB doesn't apply. This is a difficult area anyway, if this plant were the other side of a boundary fence and in an industrial park next to a farm, would you fit the RCD? I don't think any reasonable person would, so this can be considered industrial rather than farm equipment. RCDs in areas with inflammable materials or animals are fair enough, but not other areas. This has come up where on farm processing plants are built, it is a case of correct designation of the area by its use rather than its simple proximity to a farm, after all the planners use this to stop development all the time.
David
BSc CEng MIET
 06 August 2014 10:32 AM
whjohnson
Some of the stuff we work on has a number of large inverter drives, and we have found it impossible to get them to work with any kind of RCD protection.
We took the view that things like this are what the Designer's 'Departures' box is for on the forms!
Oh, and make sure all your earthing and bonding is up to scratch.
 06 August 2014 03:35 PM
What's the rating of the motor, what's the starting current and what's the RCD current rating
This may be no more than simple magnetic saturation of the RCD toroid.
The alternative may be a "proper" circuit breaker with ground fault protection
Either way - if there really is 300mA leaking then it's pretty dangerous to ignore it
 06 August 2014 04:55 PM
perspicacious
"Some of the stuff we work on has a number of large inverter drives, and we have found it impossible to get them to work with any kind of RCD protection.
We took the view that things like this are what the designer's 'Departures' box is for on the forms!"
120.3 reads: Any intended departure from these parts requires special consideration by the designer of the installation and shall be noted on the Electrical Installation Certificate specified in Part 6. The resulting degree of safety of the installation shall be not less than that obtained by compliance with the Regulations.
I'd be interested in reading the signed for technical stance confirming that the omission of a 300 mA RCD will satisfy the requirements of 705.411.1 (iii) and 705.422.7
As I'm protective of my PII, I'd ask the supplier of the VSD etc to either confirm that their device(s) will not trip a 300 mA RCD or to provide their signature on the EIC before authorising their payment.
BOD
 06 August 2014 05:11 PM
Well, it doesn't of course.
If however there really are some 300mA returning, as part of the normal design, working correctly, as ther makers intended, (I have worked with some EMC chambers and similar where to keep signals out/in this sort of current is found due to very large filter capacitances to ground)
Then the only thing you can do is to re-create an equivalent level of safety, by restoring the "multiple independent faults required to give rise to danger" condition lost when the CPC current is high enough that a single fault is dangerous.
This is no sillier than precautions to be taken for the high earth conductor currents for IT equipment.
The mitigation is multiple independent earth paths, so that any one can fail and it is not dangerous - just instead of one of your 2 or more faults before a danger arises is you RCD being jammed, it is the interruption of one of the redundant CPC.
Problems arise if its TT of course, in that you now need to guarantee a really good rod impedance at 8KHz or whatever not just 50Hz..
At that point, filtering to neutral, rather than earth, and placing the whole filtering thing inside a protective cover, as if it were a live part is an alternative. One can then have a large capacitance between neutral and earth, as there is a much lower voltage there.
This does not meet BS7671, and surprisingly many things could be done under other legislation.
For wilder examples
Chatting to others, it is not of course the 50Hz leakage that is biting you here, but the square wave at 8/16/30KHz or whatever the VSD is chopping at.
There is ~400V or more p-p square waves on each output, and you only need a fraction of a microfarad to earth to explain the current you need to fire the RCD- it also explains how lowering the frequency helps if that is possible in this case. Xc being inversely proportional to frequency and all that.
Edited: 07 August 2014 at 01:46 PM by mapj1
 06 August 2014 08:09 PM
JP,
Give me a yell tomorrow, been there ;-)
 06 August 2014 08:59 PM
paulskyrme
Just use a suitable RCD.
There may, or may not be 300mA of leakage.
Most VSD's are not designed to run on RCD's due to the harmonics filters up front.
Now, the contractor could take a suitable supply from the DB, if it's not a Schneider, or Siemens, then run it through one of their enclosures with one of their 300mA RCD's in, and job done.
After all you don't want to upset the type approval bandwagon do you!
If you want details on the RCD's you know where I am.
I've come across this when I was working for the drives manufacturer.
Our MI's said no RCD's.
Some clients insisted, so it could be done, at a price, and it's NOT cheap!
The leakage, may, well be designed in and deliberate in the drive system.
 06 August 2014 10:18 PM
Zs
As a note.. I've seen >300mA leakage before and in that case it was a ground source heat pump at the moment it kicked-in to begin sourcing heat from the ground. no huge motors or any of our usual suspects.
Stu, you've got to tell us all about it....
Zs
 06 August 2014 10:24 PM
Originally posted by: slittle
JP,
Wel Stu, don't keep it to yourself! Spill the beans.
 06 August 2014 10:26 PM
Oh I missed your request to Stu Zs. I was too busy catching up on the post!
IET » Wiring and the regulations » SECTION 705 OF THE BGB