Topic Title: fire rated downlights in 3 storey dwelling
Topic Summary: required ?
Created On: 29 April 2014 07:47 AM
Status: Post and Reply
Linear : Threading : Single : Branch
Search Topic Search Topic
Topic Tools Topic Tools
View similar topics View similar topics
View topic in raw text format. Print this topic.
 29 April 2014 07:47 AM
User is offline View Users Profile Print this message



aligarjon

Posts: 2837
Joined: 09 September 2005

Hi guys. just a quicky hopefully. is there a requirement to fit fire rated downlights in a 2 storey extension on the back of a 3 storey property ? It will be in the ground floor kitchen. i prefer to to use non-fire rated with LED'S where possible as the lamps seem to like them better.


Gary

-------------------------
Specialised Subject. The Bleedin Obvious. John Cleese
 29 April 2014 10:34 AM
User is offline View Users Profile Print this message


Avatar for Legh.
Legh

Posts: 3488
Joined: 17 December 2004

I would have thought that you would ask a few basic questions regarding likely risk such as:
1/ Is the room above the kitchen likely to be used as a bedroom?
2/ Will smoke and heat detectors be fitted?
3/ Will the open access allowed by a non-fire rated lamp holder propose a risk if a fire were to break out in the kitchen?

Legh

-------------------------
Why do we need Vernier Calipers when we have container ships?

http://www.leghrichardson.co.uk

"Science has overcome time and space. Well, Harvey has overcome not only time and space - but any objections."
 29 April 2014 10:59 AM
User is offline View Users Profile Print this message


Avatar for redtoblackblewtopieces.
redtoblackblewtopieces

Posts: 206
Joined: 10 January 2013

Also would this new build extension be subject to part e "passage of sound" if it is a bedroom or some form of wc above, I'm thinking more on the air bourne sound issue rather than impact sound ?
Kevin

-------------------------
Safety through a Standard
Compliance by Approved Documents
 29 April 2014 01:23 PM
User is offline View Users Profile Print this message



J146P

Posts: 1
Joined: 29 April 2014

Honestly, I'd recommend Fire Rated as opposed to non. Just for the extra safety measure. I know it's a long shot but it could potentially save a life/lives.
 29 April 2014 02:30 PM
User is offline View Users Profile Print this message



AJJewsbury

Posts: 11467
Joined: 13 August 2003

It's a few years old now, but this Wiring Matters article - and especially the TRADA test results - might be of interest. http://electrical.theiet.org/w...minaires.cfm?type=pdf

As I read it it, boils down to whether the ceiling concerned is required to have a 30-min or 60-min rating.

- Andy.
 29 April 2014 03:40 PM
User is offline View Users Profile Print this message



aligarjon

Posts: 2837
Joined: 09 September 2005

Cheers Guys. its a bedroom and kitchen above (small anex type thing with its own entrance as well as through the house). My first thoughts were that fire rated was not required as its no different to a normal 2 storey house in the extension part and the risks are no more here than than there. There will be smoke detectors only, no heat detectors.
i will find out about the ceiling rating Andy, thankyou for that.

Gary

-------------------------
Specialised Subject. The Bleedin Obvious. John Cleese
 30 April 2014 07:55 AM
User is offline View Users Profile Print this message


Avatar for dickllewellyn.
dickllewellyn

Posts: 1150
Joined: 19 March 2010

I tend to use open back fittings with LEDs too Jon. You can get around the fire rating part with hoods if need be. Aico make one which looks like a witches hat that I believe also complies with sound and thermal constraints, otherwise lots of companies make a basic intumescent hood that will continue a ceilings fire rating. The Aico one is the easiest to fit though I think provided you are not too near to joists.

-------------------------
Regards
Richard (Dick)

"Insert words of wisdom and/or witty pun here"