Evening ,
tested a school it failed ive done repairs ,
how do i do test sheets ?
is it minor works for the repairs ?
do i have to re-do the 30 page EICR so school has satisfactory on it
cheers
 27 April 2014 10:06 PM
Jaymack
An unsatisfactory report is a snapshot of the installation at that time, it shouldn't be altered and re-issued as satisfactory, using the same reference details after corrective work. As I understand it, corrective work requires separate certification, e.g. a MWC with a reference and attachment to the original report.
Regards
 28 April 2014 01:10 AM
mantutu
I love this industry< just saying
 28 April 2014 01:21 PM
User is online View Users Profile Print this message
AJJewsbury
I agree with Jaymack - Unsatisfactory EICR + MWC/EIC for each repair for every failure = satisfactory. If the customer wants an EICR re-doing, then they're free to commission & pay for such a thing, but it isn't necessary.
 28 April 2014 01:25 PM
AJJewsbury
Just to add - there should be no presumption or encouragement for the person/organisation doing the inspection to pick up any repair work (indeed good practice should suggest the reverse in an ideal world). So there should be no general assumption that the EICR can be 're-issued' on completion of the repairs without a re-inspection and re-test.