scottri
Hi,
I have relatively low power instrumentation mounted away from our main control panel that is grouped together, but the A.C. supply requirements are 110Vac and 230Vac.
To minimise cable runs we could like to know if we can supply both voltages, from our CP, from individual cores sharing the same cable (in an industrial plant application).
Please let me know.
Many thanks...
 27 February 2014 12:22 PM
zeeper
reg 521.7 does allow this. conductors have to be insulated for the highest voltage obviously.
 27 February 2014 01:50 PM
scottri
Many thanks zeeper...one of these days my company will pay me to sit the 17th ed...
 27 February 2014 02:34 PM
OMS
It is allowable, but my only reservation would be of isolation - you would need to be pretty certain when it comes to labelling or physical switchgear that all live conductors in the cable were isolated if/when required
Regards
OMS