Topic Title: 314. 1 - EICR
Created On: 26 February 2014 03:10 PM
Afternoon all.
Looking at an old commercial building with lots of boards, sub-boards, etc. some areas with a few offices grouped together are supplied from single phase DB's with front end 30mA RCD's.
Obviously the RCD could take out the lighting, power, etc.
So this would I presume fall foul of 314.1.
Looking through the inspections schedule, I cant actually see a box that refers to this, i.e. circuit arrangements, etc.
So, no box to put an X in.
I think I should make an observation and give a C3 but I'm not sure it should be a code at all.
Any thoughts?
Edited: 26 February 2014 at 05:01 PM by leckie
 26 February 2014 04:00 PM
Don't worry about the model inspection schedule - it's there to support a minimum standard, not constrain competence. There's plenty of room in section K of the main report.
That said, I'd consider carefully what the dangers of an RCD trip would be - is there no borrowed light, or emergency lighting? Are people unfamiliar with the layout likely to be there? We happily put all lighting on adjacent rooms not only on the same RCD but often on the same MCB in many situations - or open plan offices with several lighting circuits all controlled by a single contactor - without too much worry. If someone drove a fork-lift into the submain cable (or just overloaded it) the entire area would black out regardless of RCDs - would that be unacceptable?
 26 February 2014 05:01 PM
Yes Andy, that is what I tend to think as well, its not a actually dangerous in this case. The occupants are familiar with the building and its not a dangerous environment as such.
I don't think it is worth mentioning in this case, in a different environment then it might well be different. Thanks
 26 February 2014 06:03 PM
aligarjon
i would just mention it in the report at the end. not ideal but - - - .
Gary
 26 February 2014 06:38 PM
anastasis
This is a tricky one, because there are zillions of installs like this, and no guidance (as far as I know) on what 314.1 (and 314.2) actually mean in practice. I think you're right to take a risk-based approach.